[Equest-users] VAV Cooling Control Issues
Busman, Michael R
MBusman at chevron.com
Tue Sep 18 08:24:50 PDT 2012
Adam,
I only had a chance to very briefly look at your input file.
I noted that you have COOL-CONTROL = RESET. You might check your reset schedule or change it from reset to warmest zone and see if the unmet hours come down.
Is it just unmet cooling hours or do you also have a significant number of unmet heating hours? If so, you might try changing the thermostat type from proportional to reverse-acting.
That's about the best I can suggest at the moment.
Mike Busman
Michael R. Busman, CEM
Lead Project Engineer II
Chevron Energy Solutions
A Division of Chevron U.S.A., Inc.
145 S. State College Blvd.
Brea, CA 92821
Direct 714-671-3561
Fax 714-671-3438
eFax 866-420-0335 (Include my Full Name followed by "CAI:MHTZ" on Cover Sheet)
Mobile 310-387-2083
mbusman at chevron.com<mailto:mbusman at chevron.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Adam Gower
Sent: Monday, September 17, 2012 1:07 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] VAV Cooling Control Issues
We have a System type 5 baseline building with a lot of laboratory exhaust. The unmet cooling hours are extremely high and it appears to be a control issue. The only thing that reduces the unmet hours is to set the min flow ratio to 1, but this is obviously not correct. I have attached the .INP & .PD2 files. Any help or input would be appreciated.
Thanks
Adam
Adam Gower, EIT, Mechanical Engineer I BVH Integrated Services, P.C.
50 Griffin Road South, Bloomfield, CT 06002 I 860.286.9171
One Gateway Center, Suite 701, Newton, MA 02458 I 617.658.9008
bvhis.com<http://www.bvhis.com/> I twitter.com/bvhis <www.twitter.com/bvhis >
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120918/49f3427d/attachment-0002.htm>
More information about the Equest-users
mailing list