[Equest-users] Fuid-cooler has zero design flow

Pasha Korber-Gonzalez pasha.pkconsulting at gmail.com
Wed Sep 19 12:00:44 PDT 2012


You might not be able to link these items together (restriction of DOE-2),
you should look in the DOE-2 manuals (Volume 2) under heat rejection
equipment and see if this equipment piece will connect to a WLHP...sometime
there are little details that DOE-2 won't let happen exactly as you want it.

Hope this helps you a little.

Pasha

On Mon, Sep 17, 2012 at 9:24 AM, Miller, Jessica <JMiller at trojb.com> wrote:

> I am trying to attach a heat-rejection fluid-cooler to a WLHP
> circulation-loop but my simulation keeps crashing out at 18% and I get an
> error:****
>
> ** **
>
> Loop:  FC Water Loop CL 1 has zero design flow.  Check input for
> consistency, or specify design loads.  Does anyone know what I might be
> doing wrong?****
>
> ** **
>
> Thank you!****
>
> ** **
>
> ** **
>
> I set the following properties:****
>
> ** **
>
> "FC Loop Pump 1 CL" = PUMP            ****
>
>    ..****
>
> ** **
>
> "CL Grnd Loop 1" = CIRCULATION-LOOP****
>
>    TYPE             = LAKE/WELL****
>
>    LOOP-DESIGN-DT   = 10****
>
>    MIN-RESET-T      = 65****
>
>    ..****
>
> ** **
>
> "FC Water Loop CL 1" = CIRCULATION-LOOP****
>
>    TYPE             = WLHP****
>
>    SUBTYPE          = SECONDARY****
>
>    PRIMARY-LOOP     = "CL Grnd Loop 1"****
>
>    LOOP-OPERATION   = STANDBY****
>
>    DESIGN-HEAT-T    = 70****
>
>    DESIGN-COOL-T    = 85****
>
>    COOL-SETPT-CTRL  = FIXED****
>
>    LOOP-PUMP        = "FC Loop Pump 1 CL"****
>
>    ..****
>
> ** **
>
> SET-DEFAULT FOR HEAT-REJECTION  ****
>
>    TYPE = FLUID-COOLER****
>
>    CAPACITY         = 1.2863e+006****
>
>    NUMBER-OF-CELLS  = 1****
>
>    CAPACITY-CTRL    = VARIABLE-SPEED-FAN****
>
>    COIL-LOSS        = 252900****
>
>    DESIGN-APPROACH  = 7****
>
>    DESIGN-WETBULB   = 78****
>
>    CW-STATIC-HEAD   = 0****
>
>    CW-FLOW-CTRL     = VARIABLE-FLOW****
>
>    SPRAY-KW/CELL    = 2.2371****
>
>    ..****
>
> ** **
>
> "WLHP Fluid Cooler 1" = HEAT-REJECTION  ****
>
>    TYPE             = FLUID-COOLER****
>
>    CW-LOOP          = "FC Water Loop CL 1"****
>
>    ..****
>
> ** **
>
> *Jessica K. Miller, EIT, LEED® AP*****
>
> Associate****
>
> HVAC Engineering****
>
>
> *TRO Jung|Brannen
> *22 Boston Wharf Road
> Boston, Massachusetts  02210
>
> *t*     617.502.3400
> *f*     617.502.3401
>
> *www.trojungbrannen.com*****
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120919/f3c3c281/attachment-0002.htm>


More information about the Equest-users mailing list