[Equest-users] System sizing ratio-Table G3.1.2.2
Cam Fitzgerald
cam at energyopportunities.com
Wed Apr 3 05:44:23 PDT 2013
Good morning,
Option 2 is the appropriate way to represent the oversizing requirements in
Section G3.1.2.2. Since the supply airflow must be determined based on a 20
degree F temperature difference between the supply and room design
temperature (Section G3.1.2.8) and using the system oversizing factor will
violate this requirement unless you also adjust the temperature differential
to compensate for the fan oversizing.
Hope this helps!
Cam Fitzgerald
Energy Opportunities/a 7group company
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of GK Pandian
Sent: Wednesday, April 03, 2013 7:57 AM
To: equest-users
Subject: [Equest-users] System sizing ratio-Table G3.1.2.2
Folks,
I 'm trying to increase the equipment capacities in baseline model in order
to comply with G3.1.2.2. using below options;
System sizing ratio-Option 1
System sizing ratio-Option 2
Basic
Cooling
Heating
Basic
Cooling
Heating
1.15
1
1.08
1
1.15
1.25
Both options are looks similar, but it's giving two different results
though!
If I change the basic system sizing ratio to 1, I can see increase in
equipment capacity but not in airflow. So, I concluded to proceed with
"option 1", since I can see increase in both capacities and airflow.
Am I doing correct here? Appreciate your suggestions.
Thanks
Gopi