[Equest-users] LEED Review Comment for Appendix A constructions
Cam Fitzgerald
cam at energyopportunities.com
Fri Apr 12 04:45:11 PDT 2013
Good morning, Pasha,
Appendix G primarily provides very specific guidance for building the
appropriate Baseline model to use as a benchmark to calculate the projected
energy savings for your Proposed building as designed. Most of the guidance
in Table G3.1 for the Proposed model indicates it must be modeled as
designed. This is where appendix A comes in for the Proposed constructions.
U-values may only be calculated using the inverse of the sum of the
R-values if each layer is continuous (e.g. uninterrupted by other materials
such as steel studs or joists). Appendix A provides tables with the
effective U-values for various common heterogeneous constructions. Depending
on the construction, the overall U-value for the assembly can vary
significantly from the U-value calculated by summing the U-value of the
major components. The Appendix A assembly performance must be used for the
Proposed constructions to accurately reflect performance of the building
envelope. Hope this helps.
Have a great day!
Cam Fitzgerald
Energy Opportunities/a 7group company
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha
Korber-Gonzalez
Sent: Thursday, April 11, 2013 6:00 PM
To: eQUEST Users List
Subject: [Equest-users] LEED Review Comment for Appendix A constructions
Hi -- hopefully others have run into this before. We have a review
comment that suggests that we need to revise our Proposed Construction
performance values by reference of Appendix A constructions from 90.1
standard.
This is a new comment which I have not experienced LEED Reviewers addressing
on past projects, and it seems to be in line with the release of the new
Table 1.4 that is so interactive and also requires reference to Appendix A
tables for proposed construction performance values.
I have re-read Appendix G and cannot find any required reference to using
Appendix A performance values for proposed construction except for
Fenestration that is Not NFRC rated. Where does it state the requirement
to use Appendix A values for all of the proposed envelope construction
values?? Why is GBCI implementing this now, and it was never a factor
before?
I need some education on this one please, I couldn't find any specific
references on my own.
Thanks!
Pasha