[Equest-users] LEED Review Comment for Appendix A constructions
Nick Caton
ncaton at smithboucher.com
Fri Apr 12 13:26:45 PDT 2013
To chime in with some extra thoughts:
I've actually adopted citing Appendix A quite often for both baseline and proposed construction descriptions, before even seeing the new EAp2 spreadsheet.
If anyone has ever looked hard at the .inp files we've passed around on the lists here for baseline constructions (see attached), you'll find they include quite a few citations to Appendix A.
That particular table for various framing combinations Maria is referencing is super useful for energy modeling studies beyond LEED as well. I recall looking up the math involved to derive how steel studs circumvent batt insulation once, and let's just say I came away happy to know there's a table handy for these things =).
The best of us, modelers and reviewers alike, are learning all the time - so some degree "inconsistency" is to be expected project-to-project, and it's a 2-way street. I would expect a competent reviewer to come up with new ways to analyze and challenge documentation over time, just as I would expect a competent modeler to improve themselves and the quality of their models/documentation. I am often seeing new questions/commentary I've never seen asked before, ranging from thought-provoking to inane, but I think it's to be expected to some degree and nothing to lose sleep over.
Regards,
~NIck
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez
Sent: Friday, April 12, 2013 10:25 AM
To: Maria Karpman
Cc: eQUEST Users List
Subject: Re: [Equest-users] LEED Review Comment for Appendix A constructions
Maria & Cam---thanks for taking time to offer your guidance.
Maria--I was hoping to hear from your experience & advice. :) Cam--thanks for confirming that I'm not blind! :)
I don't have issue with the engineering theory of the topic--I understand, agree and recognize thermal bridging effects and so forth (thanks to my great engineering mentors in my younger days.)
What I was challenging specifically was that this was the first instance that this Review Comment & request for Appendix A reference has been presented on any of my LEED projects reviews---and I only am introduced to it since the inception of the new Table 1.4 which specifically points out the use of the Appendix A reference.
--(Thanks Shelia for your input also---I learned of the use of the new Table 1.4 after I painfully filled it in for a project that was modeled over a year ago. In the future I will certainly be filling this table out as I develop my LEED models as a simultaneous action from now on. I like how it is interactive and determines the correct references for us---agree with the potential for less mistakes, but I dislike how it does take significantly more time than the previous Table 1.4 which unfortunately does eat into the project budget a bit more; however if we complete the form during model development there may be potential to streamline/average the additional work from the overall project time...)--
I've now read through Section 5.5.3 and the User's Manual info and have a better understanding of the nature of the Review comment requirements. I'm still baffled as to why this issue hadn't been brought up on any of my previous project submissions as I had not changed my reporting approach from then until now---I don't discount that it is an existing requirement from prior to LEED 2009, but again it is frustrating when you think you are applying 100% compliance to your document submissions and *out of the blue* GBCI throws a new thing at us!
I respect that everything including LEED is a growing/improving process, but it has been a painful growing process since the inception of GBCI reviews.---(I just needed to vent.) If GBCI is such an authoritative review group then why didn't they have all this in place from the get go?? I'm sure I'm not the only one who dislikes getting a curve ball---As a LEED modeling veteran I thought that my submissions were closer to perfect than not---it's the perfectionist-side of me that doesn't like to be 'blind-sided' by something that didn't seem to be a factor in the game before now.
I guess today is already a productive day since I have learned something New! Thanks to all of you for sharing your time, experience & advice. This list-serve is the BEST!!
Cheers,
Pasha
On Fri, Apr 12, 2013 at 8:33 AM, Maria Karpman <maria.karpman at karpmanconsulting.net<mailto:maria.karpman at karpmanconsulting.net>> wrote:
Pasha,
Appendix A is referenced by 90.1 Section 5.5.3. It is not a new rule, and must be used for determining thermal properties of the proposed designs because many simulation tools including eQUEST cannot capture two-dimensional heat transfer (thermal bridging) of the specified constructions. Thermal bridging is an especially big factor for steel-frame constructions, where calculating overall U-value of wall assembly using weighted average properties of frame and cavity sections (parallel path method) can distort result by factor of 2+ compared to the tables provided in Appendix A (such as Table A3.3 or A9.2B). Note that Thermal bridging is accounted for in Tables 5.5-x which list the baseline constructions. For example, for climate zone 5 (Table 5.5-5) minimum insulation R-value of steel-framed walls in non-residential spaces is R-13 cavity plus R-7.5 continuous. If we do not account for thermal bridging, then the overall R-value of insulation in the cavity portion of the wall is R-20.5, and we'd expect that overall surface U-value (not accounting for gypsum board, siding, air, etc.) would be somewhere around 1/20.5=0.049 because cavity section is very wide compared to frame section. However the equivalent Assembly Maximum for the surface is U-0.064, which is what you'd get if you use tables in Appendix A to calculate thermal properties of frame/cavity portion of the wall assembly instead of parallel path method. There is a nice discussion on that in 90.1 User Manual.
Good luck with your project,
Maria
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of PKConsulting
Sent: Friday, April 12, 2013 8:55 AM
To: Cam Fitzgerald
Cc: eQUEST Users List
Subject: Re: [Equest-users] LEED Review Comment for Appendix A constructions
Thanks Cam, I couldn't find where it reads this in Table g3.1, Could you give me a page reference please? I need to provide my client with this reference info for their future projects.
Also can you explain why this hasn't been addressed on LEED projects in the past? This is the first time I have received this comment on any of my LEED submissions.
Thanks,
Pasha
Sent from my iPhone
On Apr 12, 2013, at 5:45 AM, "Cam Fitzgerald" <cam at energyopportunities.com<mailto:cam at energyopportunities.com>> wrote:
Good morning, Pasha,
Appendix G primarily provides very specific guidance for building the appropriate Baseline model to use as a benchmark to calculate the projected energy savings for your Proposed building as designed. Most of the guidance in Table G3.1 for the Proposed model indicates it must be modeled as designed. This is where appendix A comes in for the Proposed constructions. U-values may only be calculated using the inverse of the sum of the R-values if each layer is continuous (e.g. uninterrupted by other materials such as steel studs or joists). Appendix A provides tables with the effective U-values for various common heterogeneous constructions. Depending on the construction, the overall U-value for the assembly can vary significantly from the U-value calculated by summing the U-value of the major components. The Appendix A assembly performance must be used for the Proposed constructions to accurately reflect performance of the building envelope. Hope this helps.
Have a great day!
Cam Fitzgerald
Energy Opportunities/a 7group company
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez
Sent: Thursday, April 11, 2013 6:00 PM
To: eQUEST Users List
Subject: [Equest-users] LEED Review Comment for Appendix A constructions
Hi -- hopefully others have run into this before. We have a review comment that suggests that we need to revise our Proposed Construction performance values by reference of Appendix A constructions from 90.1 standard.
This is a new comment which I have not experienced LEED Reviewers addressing on past projects, and it seems to be in line with the release of the new Table 1.4 that is so interactive and also requires reference to Appendix A tables for proposed construction performance values.
I have re-read Appendix G and cannot find any required reference to using Appendix A performance values for proposed construction except for Fenestration that is Not NFRC rated. Where does it state the requirement to use Appendix A values for all of the proposed envelope construction values?? Why is GBCI implementing this now, and it was never a factor before?
I need some education on this one please, I couldn't find any specific references on my own.
Thanks!
Pasha
________________________________
No virus found in this message.
Checked by AVG - www.avg.com<http://www.avg.com>
Version: 2012.0.2240 / Virus Database: 2641/5736 - Release Date: 04/10/13
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130412/02a51b68/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130412/02a51b68/attachment-0002.jpg>
-------------- next part --------------
An embedded message was scrubbed...
From: Nick Caton <ncaton at smithboucher.com>
Subject: Re: [Equest-users] Materials for baseline design
Date: Tue, 1 Mar 2011 18:28:55 +0000
Size: 26648
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130412/02a51b68/attachment-0002.eml>
More information about the Equest-users
mailing list