[Equest-users] LEED Core & Shell questions

Patrick J. O'Leary, Jr. poleary1969 at gmail.com
Thu Aug 1 14:37:11 PDT 2013


i don't recall the page in the leed 3 manual right off hand but 1)  
tenant spaces can be modeled as proposed type (hvac/water/lighting) if 
there is a legally binding signed/or master lease agreement specifying 
the proposed requirements that all tenants must adhere to and said lease 
agreement is uploaded as part of the project documentation.  i.e. lower 
lighting lpd, increased hvac unit efficiencies/power, and water saving 
fixtures.

and 2)  there is an equest limit on the number of submeters a project 
can have, and a core/shell project requires submeters for each tenant to 
be separated out between process, lighting, and hvac, so the number of 
meters can add up quickly if you're dealing with a sizeable core/shell 
with many tenant spaces.

On 8/1/13 1:36 PM, Anthony Hardman wrote:
>
> See below
>
> *Anthony Hardman, **PE, LEED AP BD&C***
>
> Building Performance Analyst
>
> *The Green Engineer, Inc.*
>
> Sustainable Design Consulting
>
> 54 Junction Square Dr.
>
> Concord, MA 01742
>
> O: (978) 610-2801
>
> C: (720) 840-7862
>
> The Green Engineer, Inc. is a Certified B Corporation
>
> *From:*Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
> *Sent:* Thursday, August 01, 2013 7:11 AM
> *To:* eQUEST Users List
> *Subject:* [Equest-users] LEED Core & Shell questions
>
> 1. Should Tenant Spaces in LEED Core & Shell projects be modeled with 
> Appendix G systems for the Baseline, and for the Proposed as well if 
> there is no HVAC design?
>
> -OR- Should Tenant Spaces be modeled as "unconditioned" in both the 
> Baseline and Proposed? (-OR- some other option?)
>
> Finished tenant spaces should be modeled as designed with terminal 
> units placed on the tenant meter.  If unfinished, it should follow 
> Appendix G.
>
> 2. What is the intent/purpose of the requirement to model separate 
> electric meters for lighting, plug loads and process loads in the 
> Tenant Spaces? Should the cost from these meters be removed from the 
> building energy cost for EAc1 savings?
>
> Download the spreadsheet 
> <http://www.usgbc.org/resources/cs-v20-eac1-spreadsheet>, it should 
> answer your questions.
>
> 3. IF HVAC systems are modeled in the Tenant Spaces, should this 
> energy be assigned to separate meters as well?
>
> LEED Core & Shell Appendix 2 
> <http://www.usgbc.org/resources/appendix-2-core-and-shell-energy-modeling-guidelines> 
> describes how the HVAC systems should be modeled for the Core and 
> Shell Building, but not for the Tenant Spaces. Appendix 2 also 
> describes the requirement for modeling separate meters.
>
> Thank you,
>
> Bill
>
> *William Bishop, PE, BEMP, BEAP, LEED AP **|**Pathfinder Engineers & 
> Architects LLP*
>
> Oh No Mr Bill.jpgSenior Energy Engineer
>
> 134 South Fitzhugh StreetRochester, NY 14608
>
> T: (585) 325-6004 Ext. 114F: (585) 325-6005
>
> bbishop at pathfinder-ea.com 
> <mailto:wbishop at pathfinder-ea.com>www.pathfinder-ea.com 
> <http://www.pathfinder-ea.com/>
>
> PSustainability -- the forest AND the trees.P
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130801/b470f2cd/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2295 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130801/b470f2cd/attachment-0002.jpeg>


More information about the Equest-users mailing list