I believe the zone-level air flows reported in the SV-A are for a single zone.  The end of 
each line shows the ZONE MULT that gives the zone multiplier that is used by DOE-2 in 
calculating the total air flow rate that needs to be supplied by the central fans.  I'm 
not sure, but I don't think the coincidence, i.e., diversity, of these zone air flows are 
considered when they are added up.

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"


On 2/4/2013 7:57 PM, Chris Jones wrote:
> I can't recall what SV-A reports for self-sized air flows - the "single" space air flow 
> or the multiplied space air flow.  In other words does DOE2 self size the zone air flow 
> based on a single space?
>
>
>
>
> >>
> Christopher Jones, P.Eng.
> Suite 1801, 1 Yonge Street
> Toronto, ON M5E1W7
> Tel. 416-203-7465
> Fax. 416-946-1005
> email cj at enersave.ca
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130204/aa1f5392/attachment-0002.htm>


More information about the Equest-users mailing list