[Equest-users] LS-C Report showing zero area

Lijun Larry lijun.larry at gmail.com
Mon Feb 25 17:37:36 PST 2013


You should look at your LS-B for the plenum zone. Since eQUEST calculate
heat transfer within the conditioned zone and unconditioned zone separately,
heat loss through the roof should be included in the plenum zone if it's
there. 

 

 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mike Raiva
Sent: February-25-13 7:26 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LS-C Report showing zero area

 

Hello,

 

My LS-C report is showing a zero number for a building with a roof area.

 



 

I have looked at our model and I don't see where the roof is not being
picked up.

 