Kent,

I didn't notice your message was only to me. I assumed it would be a matter of seconds before others replied in the negative. The "existing conditions" caveat applies only to the envelope. You must use the Appendix G baseline systems and plants for the LEED Baseline, with the possible exception of the central plant for DES systems as you mention.

~Bill

From: Kent Beason [mailto:kbeason at estesmcclure.com]
Sent: Thursday, July 25, 2013 2:49 PM
To: 'Nick Caton'; Bishop, Bill; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] existing buildings/alterations

Thanks for the feedback.    As I asked Bill offline, and I feel it goes without saying, but never hurts to be thorough :-): this applies to the old HVAC systems too, correct?  Obtaining the old HVAC system info could be a daunting challenge unfortunately.

I've learned alot about nuances...  One area of this building is storefront (essentially 100%) single pane glass around the whole perimeter!

Kent Beason
-------------------------
office - 903 581 2291
cell - 830 609 8904

From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Thursday, July 25, 2013 1:32 PM
To: Bishop, Bill; Kent Beason; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] existing buildings/alterations

Agreed.  Take note there are a couple nuances between what's written in 90.1 and what's required by the LEED reviewership.  I believe they draw a line in the sand where if more than 50% of a project is "retrofit" vs. NC by square footage, then rotations go away.

I just had 3 LEED projects wrap up at silver/gold where in the initial submission I used thoroughly documented prescriptive baseline envelopes and 4 rotations.  The preliminary review commentary required changing the envelopes to remove the rotations and match reality instead.  The previous reality was (mostly) uninsulated grout filled block walls, single pane windows without film treatments, and zero wall insulation =D!

As a net result, each of these projects jumped way up in unanticipated modeling credits.  It was a good day.

Outside the constraints of LEED, the closer your baseline models can reflect existing realities, the better and more informative the results of your models become for a retrofit analysis.

Regards,

~Nick

[cid:489575314 at 22072009-0ABB]

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com

From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Thursday, July 25, 2013 1:17 PM
To: Kent Beason; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] existing buildings/alterations

Kent,

Yes, for existing buildings, use the wall & roof assemblies, glazing properties etc. of the existing building for the Baseline values. Also, you don't have to simulate in four orientations.

Regards,
Bill

William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114            F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>           www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P   Sustainability - the forest AND the trees. P

From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kent Beason
Sent: Thursday, July 25, 2013 1:09 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] existing buildings/alterations

This question isn't eQuest specific, but deals with 90.1 interpretation.

For an existing building, with regards to shell alterations, G3.1.5-f says that "the baseline building shall reflect existing conditions prior to any revisions that are part of the scope of work being evaluated."  Is this statement as far-reaching as I believe, indicating that U-values, SHGC etc, listed in Tables 5.5 and Appendix A are ignored in a similar way as done in the proposed, since the "baseline" in this case is a real design, rather than a hypothetical baseline?

Kent Beason
Estes, McClure & Associates, Inc.
3608 West Way
Tyler, TX 75703
-------------------------
office - 903 581 2721
cell - 830 609 8904

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130725/b74278da/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130725/b74278da/attachment-0002.jpg>


More information about the Equest-users mailing list