[Equest-users] App G model VAV w unmet loads in heating

Busman, Michael R MBusman at chevron.com
Tue Jul 30 07:58:53 PDT 2013


Matthew,

Check to make sure the thermostats are defined as reverse acting instead of direct acting.  This will allow the system to start bringing on reheat when the VAV box closes to the minimum CFM stop setting.  Otherwise, the space temperature will continue to drop.

Hope that helps.

Mike Busman


Michael R. Busman, CEM
Lead Project Engineer II

Chevron Energy Solutions
A Division of Chevron U.S.A., Inc.
145 S. State College Blvd.
Brea, CA  92821
Direct  714-671-3561
Fax     714-671-3438
eFax   866-420-0335 (Include my Full Name followed by "CAI:MHTZ" on Cover Sheet)
Mobile 310-387-2083
mbusman at chevron.com<mailto:mbusman at chevron.com>



From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matthew Baron
Sent: Tuesday, July 30, 2013 6:03 AM
To: 'equest-users at lists.onebuilding.org'
Subject: [Equest-users] App G model VAV w unmet loads in heating

HI,
I am working on several school models and they generally fall into the packaged vav with reheat category. The spaces are fine for cooling, but are way off for heating. When I look at the ss-p report the heating capacity for the units shown to be zero, when I look at the ss-a report it indicates the heating load. I have entered the hot deck temp, zone entering temp, a preheat coil. Any suggestions would be appreciated.

Thanks,
Matthew J. Baron
[wendel EM]

Wendel, 140 John James Audubon Pkwy, Suite 201, Buffalo, NY 14228
p 716.688.0766   f 716.625.6825   e mbaron at wendelcompanies. com   w wendelcompanies. com

ARCHITECTURE    ENGINEERING    PLANNING    ENERGY SERVICES    CONSTRUCTION MANAGEMENT

CONFIDENTIALITY NOTICE: This email transmission is confidential and is intended only for the person(s) named above. Its contents may also be protected by privilege, and all rights to privilege are expressly claimed and not waived.  If you have received this email in error, please call us immediately and destroy the entire email. If this email is not intended for you, any reading, distribution, copying or disclosure of this email is strictly prohibited.

Please consider the environment before printing this email.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130730/2455b53f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 3940 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130730/2455b53f/attachment-0002.png>


More information about the Equest-users mailing list