[Equest-users] Equest - Simulation Report BEPS

Nick Caton ncaton at smithboucher.com
Mon Jun 3 13:39:50 PDT 2013


Hey Ginnie,

I had to perform some shenanigans to get those files to open happily (something’s up with that .PD2 – be sure to save again from your working copy), so this may not match exactly what you’re seeing, but here’s the result I’m seeing after a trial simulation:

[cid:image002.png at 01CE606E.73ABC8B0]
74.6 kBtu/SF/Yr is the” Site” EUI:  this is what’s consumed at your project.  Site EUI is the metric I’m used to discussing with architects and building owners who are interested, and is what the 2030 challenge targets are defined around.

“Source” EUI (117.3 kBtu/SF/Yr here) accounts for losses in the production/transmission of energy… i.e. how many Btu’s of coal were burned to produce the energy delivered at your project.  A “fuzzier” metric to be sure, but I suppose of more interest to those pushing reform of our energy grid.

In eQuest, you can review the default values for the site-to-source efficiency ratio, and adjust accordingly under your electric and fuel meters in detailed mode.

That said, a quick google to check on Energystar suggests your source EUI is well below the average (169)  for K-12 schools:  http://www.energystar.gov/index.cfm?fuseaction=buildingcontest.eui.  If you were to plug in values for the project into EnergyStar’s target finder tool, as we typically would for LEED EAp2 documentation, you could produce a more site-specific EUI average value to cite, if you’re interested.

I’d maintain my original hunch that this result checks out within the range of normal expectations.  Also, here’s a corrected link to the 2030 challenge PDF I meant to share:  http://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=1&cad=rja&ved=0CC0QFjAA&url=http%3A%2F%2Fwww.architecture2030.org%2Fdownloads%2F2030_Challenge_Targets_National.pdf&ei=hvysUbaBDIu68wTp4oCAAQ&usg=AFQjCNGmNOwL0mxyAzGbpvdhHIKTHj74aw&bvm=bv.47244034,d.eWU

Hope that helps!

~Nick
[cid:489575314 at 22072009-0ABB]

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com

From: Sami, Vikram [mailto:vikram.sami at zgf.com]
Sent: Monday, June 03, 2013 2:44 PM
To: Nick Caton; John Aulbach; Ginnie Schofield; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Equest - Simulation Report BEPS

Just to reiterate Nicks point – 1 KBTU/ft2-yr is a REALLY low number – especially for source energy. Site energy typically runs much lower than source energy, and even that is normally an order of magnitude higher.

Vikram Sami
Associate Partner



ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com<mailto:vikram.sami at zgf.com>
925 Fourth Avenue, Suite 2400
Seattle, WA 98104


From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Monday, June 03, 2013 11:26 AM
To: John Aulbach; Ginnie Schofield; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Equest - Simulation Report BEPS

One extra thought:  Your expectation (<1 kBtu/SF/yr) catches my eye immediately…

If I’m not mistaken, only unconditioned warehouses have values under 1.0 for the 2030 challenge EUI targets.  I would expect any regularly occupied school to be magnitudes larger.

2030 challenge may not be on your project’s radar, but might serve a useful point of reference for what to expect.  Here’s a quick link:  www.architecture2030.org/.../2030_Challenge_Targets_National.pdf‎<http://www.architecture2030.org/.../2030_Challenge_Targets_National.pdf‎>

Best of luck!

~Nick

[cid:489575314 at 22072009-0ABB]

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com

From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Monday, June 03, 2013 11:32 AM
To: Ginnie Schofield; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Equest - Simulation Report BEPS

Yes, please post your files, Ginnie. Otherwise, all is speculation.

John R. Aulbach, PE

From: Ginnie Schofield <GSchofield at edaengineering.com<mailto:GSchofield at edaengineering.com>>
To: "equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>" <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Sent: Monday, June 3, 2013 9:08 AM
Subject: [Equest-users] Equest - Simulation Report BEPS

Equest Users:

I am modeling a school building, and on this BEPS report for baseline run and parametric runs,
the Total Source Energy KBTU/SQFT-YR
Gross-Area and Net-Area number is higher than expected.
Actually, I would expect it to be quite a bit lower in the 0.75 range.

Anyone have some approach I could follow to verify these and what could be driving this
elevated number.   I could post INP and PD2 files if necessary.

Any and all suggestions are sincerely appreciated, and thank you in advance.

GINNIE SCHOFIELD
ENGINEERING DESIGN ASSOCIATES
1607 CY Ave, Ste 303, Casper, WY 82604
(Ph) 307-266-5033   (Fx) 307-234-3805




_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>


________________________________
The contents of this email and any attachments to it contain confidential and/or legally privileged information from Zimmer Gunsul Frasca Architects LLP or its affiliates. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, be aware that any disclosure, copying, distribution, or use of the information contained herein is strictly prohibited. If you received this transmission in error, please contact the sender and destroy the material in its entirety, whether in electronic or hard copy format.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130603/c488cbce/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 28142 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130603/c488cbce/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130603/c488cbce/attachment-0002.jpg>


More information about the Equest-users mailing list