Brian:
Thanks for the comments. I was thinking that I might use the preheat option to
simulate heat returned from the borrowing systems. Any way to cool the exhaust
air so that the ERV can precondition the outside air in the summer?
Regards,
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com
________________________________
From: Brian Fountain <bfountain at greensim.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>; Rick Goeres <RickG at musgrovepa.com>;
equest-users at lists.onebuilding.org
Sent: Thu, June 6, 2013 2:53:30 PM
Subject: RE: [Equest-users] Fw: ERV on OA-From-System Comments from Jeff Hirsch
I will jump into this thread late. What the OA-FROM-SYSTEM keyword does in
DOE-2 is to set the incoming outdoor air temperature of the system using the
keyword (the borrowing system) equal to the return air temperature of the system
it specifies it is getting its OA from (the lending system). That is all. Thus
there is no real transfer of air using this keyword.
Regarding using an ERV with the OA-FROM-SYSTEM keyword, the “air” is not
returned to the lending system (see above) so there is no or little heat to
recover in the exhaust airstream. There are 2 possible workarounds for this. I
have used the frost control “preheat exhaust” in the ERV keywords to set the
exhaust temperature from which heat can be recovered. I then use electric
heating for this exhaust preheat and put that preheat on a separate, zero cost,
electrical meter. I then compare the heat added on the dummy meter to the
internal gains in the actual space to ensure they are comparable. Alternately,
you could add a dummy internal load in the lending system space to increase the
exhaust air stream temperature to give you your heat for heat recovery.
From:equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Tuesday, June 04, 2013 4:01 PM
To: Rick Goeres; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Fw: ERV on OA-From-System Comments from Jeff Hirsch
Rick:
Thanks for the response. I have tried what you are suggesting and have not been
successful in modeling the same energy recovery results that manual calculations
indicate should be achieved. It seems to me that the return airflow is from the
zone that the DOAS is attached to and not the other zones, as indicated by the
return air temperature. In other words, it lloks like the only heat availabe
for recovery is from the zone or dummy zone served by the DOAS.
I would be interested in looking at one of your projects if you care to share
one.
If the eQuest developer, Jeff Hirsh tells me that an OA-From with an ERV is not
supported, I will have to take him at his word. He did not say what aspect is
not supported. Like I said, in the past I have chopped up the ERV and attached
a smaller one to each system served and achieved the results that my manual
calculations indicated would be achieved. I am just at a loss with a DOAS that
has chilled and hot water coils as well as an ERV, since the coils have been
sized assuming that the ERV conditions the air previous to it entering the
coils.
Without the ERV on the DOAS my discharge air temperature in the winter
(Westfield, MA) is as low as 30 degrees and the chilled beams, modeled as IU,
cannot supply the required discharge air temperature. If I try to remove the
coils from the DOAS and chop them up and increase the heating/cooling capacity
of each chilled beam system, my discharge air off the DOAS drops as low as -5 in
the winter and again the chilled beams with their mini ERV's cannot condition
this air.
Any ideas?
Thank you,
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com
________________________________
From:Rick Goeres <RickG at musgrovepa.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>; equest-users at lists.onebuilding.org
Sent: Tue, June 4, 2013 11:06:19 AM
Subject: RE: [Equest-users] Fw: ERV on OA-From-System Comments from Jeff Hirsch
I have specified a DOAS as a single zone unit before and then designated it as
the OSA From System in all of the other HVAC systems. If I leave the Design
Outdoor Air and Exhaust flow inputs empty under the heat recovery tab, the
outside air from the other HVAC systems does not show up in the ERV. But if I
total the design outside air values and then input these into the Design Outdoor
Air and Exhaust flows, the ERV works and seems to be representative.
Rick Goeres, PE, LEED AP
MUSGROVE ENGINEERING, P.A.
Web: www.musgrovepa.com
234 S. Whisperwood Way, Boise, ID 83709
Ph: 208.384.0585 x324 Fx:208.384.0765
Over 35 Years of Engineering Excellence
From:equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Monday, June 03, 2013 5:54 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fw: ERV on OA-From-System Comments from Jeff Hirsch
Stormy:
In the past when I have modeled just an DOAS that did not have any heating or
cooling capacity with and ERV was to add an ERV to each zone system that the
DOAS fed. I used the same kw/cfm that the DOAS system had. So I chopped up the
DOAS with it's ERV into smaller ERV's on each system. This seemed to work good.
The problem with the project that I am working on now, is that the DOAS feeds
chilled beams. The DOAS chilled water coil and heating coil is sized in the
design with the assumption that and ERV is conditioning the outside air. The
DOAS has to dehumidify the air because the chilled beams cannot remove moisture
as there is no provision for condensate removal. If I remove the ERV from the
DOAS, the chilled and hot water coils are not large enough to condition the OA
before it reaches the ERV on the chilled beams and I can't add a chilled or hot
water coil to the ERV's on the chilled beams. So I loose the additional
heat/cool capacity designed into the DOAS.
Confusing.
Regards,
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com
________________________________
From:Stormy L. Shanks <shankssl at kjww.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>
Sent: Mon, June 3, 2013 7:15:24 PM
Subject: RE: [Equest-users] ERV on OA-From-System Comments from Jeff Hirsch
Wow, thank you for sharing that. That’s definitely a bummer. I just did a test
on a model that I did with DOAS where I had defined an ERV in the DOAS system. I
deleted the ERV from the system, and my energy was lower than when the ERV was
included. Not good. I should have known better. I suppose I will start modeling
ERV/DOAS settings in spreadsheets outside of eQUEST. Or in other software.
Stormy L. Shanks, PE
Mechanical Engineer
2882 106th St, Des Moines, IA 50322
D 515.334.4315
web | Facebook | Twitter | LinkedIn
From:equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Monday, June 03, 2013 5:17 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] ERV on OA-From-System Comments from Jeff Hirsch
Just wanted to share an e-mail from Jeff. I did not know that an ERV on a
OA-From system was not supported by eQuest. That explains why I could never get
the correct airflows on this type of design.
Unfortunately almost every project I work on does specify a VAV DOAS with an ERV
to supply ventilation air to some type of HVAC system, such as VRF indoor coils,
chilled beams or PTHP units. I will have to try the work around Jeff suggested.
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com
----- Forwarded Message ----
From: Jeff Hirsch <James.J.Hirsch at gmail.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>
Sent: Mon, June 3, 2013 12:17:58 PM
Subject: Re: [Equest-users] OA From System Question
Setting your OA system (ERU1) to be vav and having the ERV on it will not work
correctly. If you need ERV you must place your ERV in the IU system and use
that system to supply the conditioned OA. ERV on a OA-FROM system is not
supported. VAV on an OA-FROM system is possibly not what you want but I cannot
tell what you are trying to do. An IU system has a central constant volume air
supply with each zone then having zone coil to do the zone thermostat controlled
conditioning via room air flow induced as a constant ratio supply air fro the IU
(the induction-ratio). So it seems you can use the IU system as your ERU system
supplying the zones. If there is some other reason you used an OA-FROM system,
then perhaps my suggestions don’t apply, but the ERV and VAV comments always
apply.
________________________________
Jeff Hirsch
James J. Hirsch & Associates
12185 Presilla Road - Camarillo, CA 93012-9243 USA
phone: (805) 553-9000 mobile: (805) 532-1045 fax: (805) 532-2401
email: James.J.Hirsch at gmail.com
From:Paul Diglio
Sent:Monday, June 03, 2013 6:11 AM
To:equest-users at lists.onebuilding.org
Subject:[Equest-users] OA From System Question
Morning:
I am trying to model a chilled beam system as induction units. The primary air
is supplied by an ERU. I set the outside air to 0 on the chilled beams HVAC
systems tab.
In the chilled beam zone tab I set the outside air to the primary CFM and the
overall CFM to the induced air flow.
Per the eQuest help menu, "The sum of the OA requirements for all SYSTEMs that
reference an OA-FROM-SYSTEM is used to set the referenced OA-FROM-SYSTEM value
for MIN-OUTSIDE-AIR, SUPPLY-FLOW as well as adjust the referenced OA-FROM-SYSTEM
directly served ZONE maximum and minimum flows for both heating and cooling."
But per my hourly reports, the ERU is not supplying the necessary amount of
primary air and in the summer the ERU flow drops to .01 CFM.
Attached are the project files. Any ideas?
Thank you,
Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
www.pdigliollc.com
________________________________
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
________________________________
This message and any attachments contain information intended for a specific
party and may include sensitive or confidential material. If you are not the
intended recipient, please do not read, copy, use, or disclose to others. Please
notify the sender of the delivery error by reply and then permanently delete
this message and all attachments.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130606/4e9c2d4b/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1803 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130606/4e9c2d4b/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 346 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130606/4e9c2d4b/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 9229 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130606/4e9c2d4b/attachment-0002.png>
More information about the Equest-users
mailing list