Set the fan schedule value to "0" - this tells the fan to run in an
unoccupied fashion, i.e. off under most conditions.
Then under System Parameters > Fans > Night Cycle Control select Cycle on
Any. This will tell the system to use the fan whenever the thermostat
setpoint is not being met, but otherwise it will remain off.
-Robby
On Tue, Mar 5, 2013 at 1:08 PM, Jay M <fd111441 at hotmail.com> wrote:
> Hi all,
>
> How do i set the fan schedule to only be on when cooling or heating
> demands are required?
>
> In DD edit, fan schedule... I can only put "0" or "1"... if i put "0"
> then the system is off and never Cools or Heats when heating or cooling is
> needed.
>
> When I put "1" the fan is always on even when no heating or cooling is
> needed.
>
> As a result for some hours I would get the fan running when the AC/Heater
> is off.
>
> I am currently forced to put "1" for all hours for fan schedule...
>
> this ensures my AC/Heater will heat/cool the room when it is needed. But
> during idle hours... the Fan is using power to run according to "fan power
> consumption" output...
>
>
> What value should i put in the fan schedule besides "0" or "1" to fix this
> problem?
>
>
>
> Thanks!
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130305/444f849e/attachment-0002.htm>
More information about the Equest-users
mailing list