[Equest-users] How do I set Fan schedule To only meet loads?
Robby Oylear
robbyoylear at gmail.com
Tue Mar 5 13:24:39 PST 2013
Correct, -1 does not allow the fan to run for any reason. I'm fairly sure
the reason his system is not running at all is that when you give the fan
schedule a value of 0, it considers that to be "night time" or unoccupied.
If you don't allow the system to cycle on under Night Cycle Control then
it will stay off, even with a value of zero.
-Robby
On Tue, Mar 5, 2013 at 1:21 PM, John Aulbach <jra_sac at yahoo.com> wrote:
> Others please correct me, but as I recall, -1 is the only ALWAYS OFF
> input. 0 has the fan off unless the setback temperature settings are
> succedded.
>
> TRY -999. This is what is used in Optimim Star-Stop. It may work in your
> case.
>
> John Aulbach
>
> *From:* Jay M <fd111441 at hotmail.com>
> *To:* "equest-users at lists.onebuilding.org" <
> equest-users at lists.onebuilding.org>
> *Sent:* Tuesday, March 5, 2013 1:08 PM
> *Subject:* [Equest-users] How do I set Fan schedule To only meet loads?
>
> Hi all,
>
> How do i set the fan schedule to only be on when cooling or heating
> demands are required?
>
> In DD edit, fan schedule... I can only put "0" or "1"... if i put "0"
> then the system is off and never Cools or Heats when heating or cooling is
> needed.
>
> When I put "1" the fan is always on even when no heating or cooling is
> needed.
>
> As a result for some hours I would get the fan running when the AC/Heater
> is off.
>
> I am currently forced to put "1" for all hours for fan schedule...
>
> this ensures my AC/Heater will heat/cool the room when it is needed. But
> during idle hours... the Fan is using power to run according to "fan power
> consumption" output...
>
>
> What value should i put in the fan schedule besides "0" or "1" to fix this
> problem?
>
>
>
> Thanks!
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130305/b385deb9/attachment-0002.htm>
More information about the Equest-users
mailing list