[Equest-users] FW: Roof conduction (Pitch Roof)
Chris Jones
cj at enersave.ca
Thu Mar 14 14:51:02 PDT 2013
The SPACE definition should defined ZONE-TYPE = PLENUM, not
UNCONDITIONED. The ZONE definition should be TYPE = PLENUM, again
not UNCONDITIONED.
Note PLENUMs can also be defined with the SPACE definition as
ZONE-TYPE = CONDITIONED in the case of an atrium being used as a
return air plenum with lights, occupants, etc.
>Good morning,
>
>For my model, when I go to report LS-C, Is not showing any roof
>conduction, not really sure why since I have a pitch roof as
>unconditioned attic/plenum, therefore there should be heat transfer
>from the outside to the attic and from the attic to the interior space.
>
>How should I correct this?
>
>Thanks.
>
>Catalina Caballero, AIA. Assoc., LEED GA.
>Johnson, Avedano, Lopez, Rodriguez & Walewski
>Engineering Group, Inc.
>2510 NW 97th Avenue, Suite 220, Miami, Florida 33172
>Tel. (305) 594-0660 Ext. 217 Fax (305) 594-0907
>Visit us online: <http://www.jalrw.com/>www.jalrw.com
>
>JALRW Logo
>
>HVAC - Electrical - Plumbing - Fire Protection
>Sustainable Development - Commissioning
>
>This email and any files transmitted with it are confidential and
>are intended solely for the use of the individual or entity to which
>they are addressed. If you are not the intended recipient or the
>person responsible for delivering the email to the intended
>recipient, be advised that you have received this email in error and
>that any use, dissemination, forwarding, printing, or copying of
>this email is strictly prohibited.
>
>
>
>
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130314/fa48d07f/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: e959a.jpg
Type: application/octet-stream
Size: 4129 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130314/fa48d07f/attachment-0002.obj>
More information about the Equest-users
mailing list