[Equest-users] FW: Roof conduction (Pitch Roof)

Chris Jones cj at enersave.ca
Fri Mar 15 03:46:40 PDT 2013


Catalina,
I am not sure about the Wizard mode, I haven't used it that much.  I 
tend to use the Detailed edit mode or direct edit in the .inp file.

At 06:14 PM 3/14/2013, you wrote:
>Chris, where can  set this up in the wizard mode?
>
>From: Chris Jones [mailto:cj at enersave.ca]
>Sent: Thursday, March 14, 2013 5:51 PM
>To: Caballero, Catalina; equest-users at lists.onebuilding.org
>Subject: Re: [Equest-users] FW: Roof conduction (Pitch Roof)
>
>The SPACE definition should defined ZONE-TYPE = PLENUM, not 
>UNCONDITIONED.  The ZONE definition should be TYPE = PLENUM, again 
>not UNCONDITIONED.
>
>Note PLENUMs can also be defined with the SPACE definition as 
>ZONE-TYPE = CONDITIONED in the case of an atrium being used as a 
>return air plenum with lights, occupants, etc.
>
>
>
>
>
>
>Good morning,
>
>For my model, when I go to report LS-C, Is not showing any roof 
>conduction, not really sure why since I have a pitch roof  as 
>unconditioned attic/plenum, therefore there should be heat transfer 
>from the outside to the attic and from the attic to the interior space.
>
>How should I correct this?
>
>Thanks.
>
>Catalina Caballero, AIA. Assoc., LEED GA.
>Johnson, Avedano, Lopez, Rodriguez & Walewski
>Engineering Group, Inc.
>2510 NW 97th Avenue, Suite 220, Miami, Florida 33172
>Tel. (305) 594-0660 Ext. 217 Fax (305) 594-0907
>Visit us online: <http://www.jalrw.com/>www.jalrw.com
>
>JALRW Logo
>
>HVAC - Electrical - Plumbing - Fire Protection
>Sustainable Development - Commissioning
>
>This email and any files transmitted with it are confidential and 
>are intended solely for the use of the individual or entity to which 
>they are addressed. If you are not the intended recipient or the 
>person responsible for delivering the email to the intended 
>recipient, be advised that you have received this email in error and 
>that any use, dissemination, forwarding, printing, or copying of 
>this email is strictly prohibited.
>
>
>
>
>_______________________________________________
>Equest-users mailing list
><http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org 
>
>To unsubscribe from this mailing list send  a blank message to 
><mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130315/d6d02dcd/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 2d4b430.jpg
Type: application/octet-stream
Size: 4129 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130315/d6d02dcd/attachment-0002.obj>


More information about the Equest-users mailing list