[Equest-users] Splitting Zones
Andersen, Stephanie
SAndersen at dbrinc.com
Thu May 2 06:43:53 PDT 2013
Good deal. You both have saved me a lot of headache!
Thanks so much!
Stephanie Andersen
Mechanical Designer
[DBR-for Email Signature]
v. 210.546.0200 | www.dbrinc.com
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Thursday, May 02, 2013 8:32 AM
To: Andersen, Stephanie; Nick Caton; equest-users at lists.onebuilding.org
Subject: RE: Splitting Zones
Yes. ASHRAE Standard 90.1, Table G3.1, No. 7 describes the conditions that must be met to allow creating a thermal block from different HVAC zones. Condition c. is "All of the zones are served by the same HVAC system or by the same kind of HVAC system."
Regards,
Bill
William Bishop, PE, BEMP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: Andersen, Stephanie [mailto:SAndersen at dbrinc.com]
Sent: Thursday, May 02, 2013 9:16 AM
To: Nick Caton; Bishop, Bill; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: Splitting Zones
Will combining the areas work for a LEED model?
-Stephanie
Stephanie Andersen
Mechanical Designer
[DBR-for Email Signature]
v. 210.546.0200 | www.dbrinc.com<http://www.dbrinc.com>
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Wednesday, May 01, 2013 5:25 PM
To: Bishop, Bill; Andersen, Stephanie; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: Splitting Zones
I agree with Bill.
If you intend split the zone regardless in detailed edits, the attached illustrated guide from some time back may prove useful =).
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Wednesday, May 01, 2013 4:51 PM
To: Andersen, Stephanie; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Splitting Zones
Stephanie,
If the RTUs are identical, or at least of similar efficiency, my preference would be to combine their capacities, airflows etc. and model them as one unit/system. It is possible, but time-consuming to add zones once you have made changes in DD Edit mode. Be sure to Save-As the model to work from a new copy if you experiment with modifying the geometry/zones in DD Edit mode.
Regards,
Bill
William Bishop, PE, BEMP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Andersen, Stephanie
Sent: Wednesday, May 01, 2013 5:28 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Splitting Zones
All,
I'm needing to split one thermal zone into 2 thermal zones. Originally the whole space was to be conditioned by one rooftop unit, and now we have 2 units serving the space. Is it possible to split a space in half?
Thanks!
Stephanie Andersen
Mechanical Designer
[DBR-for Email Signature]
v. 210.546.0200 | www.dbrinc.com<http://www.dbrinc.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130502/7a509d1b/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 3660 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130502/7a509d1b/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 3660 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130502/7a509d1b/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130502/7a509d1b/attachment-0008.jpg>
More information about the Equest-users
mailing list