[Equest-users] Building area method ASHRAE 90.1
Nick Caton
ncaton at smithboucher.com
Mon May 6 08:36:50 PDT 2013
Hi Robert,
(Assuming 90.1-07)
With the BAM figure for multifamily @ 0.7, I expect you'll come ahead using space-by-space. Trick is to apply the most appropriate entry for each space type/function.
COMcheck is a real fast way to get a handle on what your options are - strongly recommend giving this a try.
Here's a quick listing (1 minute effort) of entries I'd expect would apply to a typical residential project - most are >0.7:
[cid:image003.png at 01CE4A44.10F423B0]
If there's a large garage, you might be able to swing "workshop" at 1.9 W/SF but that may be a stretch ;).
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of RobertWichert
Sent: Saturday, May 04, 2013 3:43 PM
To: equest-users at lists.onebuilding.org; Gina Rodda
Subject: [Equest-users] Building area method ASHRAE 90.1
To bring up a topic from a year ago (below) I have a question about using the Space by Space approach with a multi-family building. There is a BAM Category for Multi-Family, but not a Space by Space category for multi-family (except for dormitories).
Is there a work-around for space by space with multi-family?
I apologize if this has been covered before.
On a working Saturday.
--
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
Nick Caton
ncaton at smithboucher.com<mailto:equest-users%40lists.onebuilding.org?Subject=Re%3A%20%5BEquest-users%5D%20Building%20area%20method%20ASHRAE%2090.1&In-Reply-To=%3CECDF361A89E5FA479BE7E64C658B52050D8E2006%40SANDBINC4.sbi.smithboucher.com%3E>
<mailto:equest-users%40lists.onebuilding.org?Subject=Re%3A%20%5BEquest-users%5D%20Building%20area%20method%20ASHRAE%2090.1&In-Reply-To=%3CECDF361A89E5FA479BE7E64C658B52050D8E2006%40SANDBINC4.sbi.smithboucher.com%3E>
Wed May 23 17:57:42 PDT 2012
* Previous message: [Equest-users] Building area method ASHRAE 90.1 <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2012-May/011648.html>
* Next message: [Equest-users] Building area method ASHRAE 90.1 <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2012-May/011643.html>
* Messages sorted by: [ date ]<http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2012-May/date.html#11649> [ thread ]<http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2012-May/thread.html#11649> [ subject ]<http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2012-May/subject.html#11649> [ author ]<http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2012-May/author.html#11649>
________________________________
David's summary looks pretty good to me!
I want to emphasis a great point that came up along the way: Space by space can result in more LEED points by 'padding the baseline,' sure... But "real" savings result from closely reviewing the proposed design, which in turn generates opportunities to identify specific means of design improvement.
I'll share a related strategy. Consider: Engaging the lighting designer and improving design doesn't require tallying the space-by-space totals. If I recognize significant improvements can be made with revised layouts, fixture reselection, and/or tweaked control schemes, I have found it VERY productive to simply share with the lighting designer (and design team leaders, if necessary) posed scenarios: "If you can reduce your installed watts by just 10%, the LEED models will earn 2 more LEED points." "If you define your astronomical timeswitch to shut off non-critical lighting after 2AM, the project earns a LEED point." Such 'carrot on a stick' proposals normally get the intended results with minimal friction, engage the designers in a positive way ("Hey, I just earned the easiest LEED point ever!") and performing the exploratory simulations to compose these proposals can be a lot less effort on the modeler relative to a standard-focused space-by-space analysis (I'm thinking of big buildings).
>From another perspective: Some of us lighting designers are sensitive creatures =D... We may have a tough exterior, but deep inside it hurts my poor fragile feelings if someone claims "Standard XYZ states bla-bla-bla and therefore you suck at your job." This advice applies to designers of any discipline, of course. If you want to pursue improving design with a standards-centric base, be mindful of this possibility. Making everyone happy to be working with an energy modeler can be quite a challenge, but the results are rewarding. Hope that was illuminating! ~Nick
[cid:489575314 at 22072009-0ABB<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>] NICK CATON, P.E. SENIOR ENGINEER Smith & Boucher Engineers 25501 west valley parkway, suite 200 olathe, ks 66061 direct 913.344.0036 fax 913.345.0617 www.smithboucher.com<http://www.smithboucher.com> From: equest-users-bounces at lists.onebuilding.org<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
[mailto:equest-users-bounces at lists.onebuilding.org<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>] On Behalf Of David Eldridge Sent: Wednesday, May 23, 2012 4:54 PM To: eQuest Users Subject: Re: [Equest-users] Building area method ASHRAE 90.1
Patrick, the space-by-space LPD aren't mandatory requirements, so you'd be able to trade lighting power through space-by-space or BAM. Someone will have to perform the take-off either way to calculate the BAM weighted LPD for the Proposed case, so you aren't saving much time on the Proposed model. (Only saving the time to actually assign the Watts to the zone in the model.) There will be a small time savings in Baseline model creation by not determining and entering space-by-space power usage into the model. I agree with Bill that 90.1's wording about "...if a lighting design exists..." points me towards space-by-space if at all possible. But GBCI seems to accept both, regardless of possible BAM inaccuracies which as Nick pointed out may or may not be significant, so the main result of this gigantic thread is:
1. Use the same method in both cases.
2. Several people think 90.1 suggests space-by-space if the lighting system is designed.
a. Not always (ever?) enforced/requested by GBCI.
b. When the model is being used to inform the design or calculate incentives, this is the more accurate approach if there is variance in the spaces for control types, LPD values, and occupancy schedules.
3. Although BAM may not provide the most accurate predictions of energy usage, it may still be "legal" for EAC1 point calculation purposes.
David David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP Grumman/Butkus Associates
From: equest-users-bounces at lists.onebuilding.org<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org><mailto:equest-users-bounces at lists.onebuilding.org<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>> [mailto:equest-users-bounces at lists.onebuilding.org<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>] On Behalf Of Patrick J. O'Leary, Jr. Sent: Wednesday, May 23, 2012 2:41 PM To: Bishop, Bill Cc: eQuest Users; Oscar B.
Subject: Re: [Equest-users] Building area method ASHRAE 90.1 referencing this comment: "The only obvious case for using the Building Area Method to determine modeled LPD is the case that Nick mentioned where lighting neither exists nor is specified." or when the lighting designer/electrical engineer has higher lighting densities that exceed one (or more) of the space-by-space maximum allowable lpds but compensates for it by having lower lpds in other spaces such that the whole building lpd does not exceed the maximum allowable by the whole building method.
On 5/23/12 7:45 AM, Bishop, Bill wrote: Building Area and Space-by-Space are not methods for designing lighting systems. They are prescriptive requirements for demonstrating lighting energy compliance in 90.1. The LPD allowances in Tables 9.5.1 and 9.6.1 do not need to be complied with if using energy modeling to demonstrate compliance for 90.1 and for LEED. (Only the Mandatory Provisions of 9.4 need to be met for the lighting design.) Energy modelers only need to know the lighting power and space use categorizations of the design as shown on the drawings (along with schedules and controls), not the process used to design it (which typically considers light levels in footcandles or lux).
I think that if a lighting system has been designed, a strong argument can be made that the space-by-space method needs to be used in both the proposed and baseline cases, and that lighting power needs to be entered individually for each space/zone. "If construction documents are complete, the proposed building lighting system power is modeled as shown on the design documents." (ASHRAE 90.1 User's Manual, p. G-17) "The LPD for the proposed design is taken from the design documents for the building. The LPD specified in the models must correspond to the spaces within each thermal block." (ASHRAE 90.1 User's Manual, p. 11-14 and also p. G-18) The only obvious case for using the Building Area Method to determine modeled LPD is the case that Nick mentioned where lighting neither exists nor is specified. As Maria Karpman, Nick and Patrick have mentioned, you are likely to show higher energy savings using the Space-by-Space method. Beyond that, using Space-by-Space allows you to give valuable feedback to the design team, which I would argue is a responsibility of energy modelers. It is routine for me to point out areas of potential improvement of the lighting design in every project I model, based on the allowances in Table 9.6.1. "Yes, Ms. Architect, that is a lovely looking light fixture, but 2.6 W/ft2 of lounge lighting is more than twice the baseline allowance." I don't know how you give helpful feedback if you are just comparing two building-averaged lighting power densities. Regards, Bill -
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130506/10bc0cf7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130506/10bc0cf7/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 14059 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130506/10bc0cf7/attachment-0002.png>
More information about the Equest-users
mailing list