Ivan ??????????
The only difference between the different azimuths is the solar radiation.
I think you should compare the summary loads report (LS-E by space, or
LS-F for the whole building) for the different orientations and see how
much the solar heat gains, especially through the windows, change. If
you really want to get into it, you can also print out hourly reports
for the solar heat gains, heating and cooling loads for the ground floor
zones. You can also switch weather files and see what happens. I will
send you by e-mail a different weather file for Wuhan that I've created.
Good luck.
Joe
Joe Huang ??
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com
http://www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 5/22/2013 7:02 PM, Yf Sun wrote:
> Hi dear equesters!
> I was doing orientation study on my office module i can not figure out
> why i got 26% OF HOURS OUTSIDE OF THROTTLING RANGE in BEPU report when
> i set the azimuth at 15 degrees for ground floor, the system worked in
> throttling range when azimuth at 10 or 20 degrees! the weather file i
> used is CTYW Wuhan (china).
>
> I attached the model, reports and the weather file. Any help will be
> appreciated!
>
>
> --
> Best regards
> ???
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130522/363986dd/attachment-0002.htm>
More information about the Equest-users
mailing list