[Equest-users] Induction Ratio Question

Bishop, Bill bbishop at pathfinder-ea.com
Tue May 28 10:56:38 PDT 2013


Paul,

You can modify the Induction Ratio on the Systems -> Fans -> Flow Parameters tab for each IU system. IU systems have an INDUCTION-RATIO of 3.0 by default.

Regards,
Bill

William Bishop, PE, BEMP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114            F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>           www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P   Sustainability - the forest AND the trees. P

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Tuesday, May 28, 2013 1:01 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Induction Ratio Question

The eQuest Help menu states:
INDUCTION-RATIO

For IU systems only, the ratio of induced air flow to primary air flow. This entry is applicable to the IU system type, but not to the variable-ratio ceiling induction units used for subzone temperature control (SZCI system type), which have a preprogrammed value of 1.0. The value input for INDUCTION-RATIO applies to all zones in the system.



Can anyone tell me where to enter the Induction Ratio?



Thank you,

Paul Diglio, CEM, CBCP
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082

www.pdigliollc.com<http://www.pdigliollc.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130528/342a48d0/attachment-0002.htm>


More information about the Equest-users mailing list