[Equest-users] Appendix G Baseline Systems 6 and 8 - supply air temperature controls?

Bishop, Bill bbishop at pathfinder-ea.com
Thu Nov 21 10:13:35 PST 2013


ASHRAE Standard 90.1, G3.1.3.12 requires cooling supply air temperature reset for Systems 5 through 8.
G3.1.3.14 requires "supply air temperature setpoint shall be constant at the design condition" for Systems 6 and 8.
How should we interpret this and model it in eQUEST (for Systems 6 and 8)?

If the "design condition" in G3.1.3.14 means "peak design flow rate", I suggest the following cooling control settings:

-             COOL-CONTROL     = WARMEST

-             COOL-MIN-RESET-T = 56                    $ (assumes 76F cooling T-stat; 56F MIN-SUPPLY-T for 20F difference per G3.1.2.8)

-             RESET-PRIORITY   = AIRFLOW-FIRST

-             COOL-MAX-RESET-T = 61                   $ (5F reset per G3.1.3.12; assumes 76F cooling T-stat)

Using a RESET-PRIORITY of "TEMP-FIRST" resets the supply air temperature before the airflow, which does not satisfy the G3.1.3.14 requirement.
Using a RESET-PRIORITY of "TEMP-FIRST" or "SIMULTANEOUS" does not satisfy the G3.1.3.12 requirement, since temperature is reset well  before minimum cooling load conditions are reached.

Does anyone have an alternative/additional suggestion or interpretation?

Thanks,
Bill

William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[webCertified_logo_colorRGB72DPI.jpg]



134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 325-6004 Ext. 114            F: (585) 325-6005

bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>           www.pathfinder-ea.com<http://www.pathfinder-ea.com/>

P   Sustainability - the forest AND the trees. P



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131121/5aac4c04/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131121/5aac4c04/attachment.jpg>


More information about the Equest-users mailing list