[Equest-users] Cooling coil leaving temp error
Hall, Brendan
BHall at karpinskieng.com
Tue Nov 5 13:34:00 PST 2013
I would say that is the likely culprit. The commonly used keyword is zone entering temperature (MIN-SUPPLY-T), not the coil leaving temperature. The coil temperature will be variable depending on how much heat gain the fan provides and the throttling range of the coil controller. In this case, the coil leaving temperature would likely be around 50 degrees if you have that much fan gain and I could see that generating that error. 5 degrees is on the high side for a fan, so check what number you are using to determine what the power input is. I always use the bhp not the nameplate to determine the kw/cfm of the fans.
Brendan Hall, PE, LEED AP BD+C
Engineer, Mechanical
karpinski
ENGINEERING
3135 Euclid Avenue
Cleveland, OH 44115
P 216.391.3700<tel:216.391.3700> Ext 3111
E bhall at karpinskieng.com<mailto:bhall at karpinskieng.com>
W www.karpinskieng.com<http://www.karpinskieng.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Tuesday, November 05, 2013 4:02 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Cooling coil leaving temp error
I'm running a simulation where I get the following error:
In EL1 Sys1 (VAVS) (G) , cooling coil leaving temperature must
be at least 6F higher than entering water temp.
I checked my temps - the entering water temp is 44 degrees, and the coil leaving temp is 55. I have a 5 degree delta T on the fan - could that be causing this?
Vikram Sami
BEMP, LEED BD+C
Associate Partner
ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com<mailto:vikram.sami at zgf.com>
925 Fourth Avenue, Suite 2400
Seattle, WA 98104
________________________________
The contents of this email and any attachments to it contain confidential and/or legally privileged information from Zimmer Gunsul Frasca Architects LLP or its affiliates. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, be aware that any disclosure, copying, distribution, or use of the information contained herein is strictly prohibited. If you received this transmission in error, please contact the sender and destroy the material in its entirety, whether in electronic or hard copy format.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131105/1dddf6a7/attachment-0001.htm>
More information about the Equest-users
mailing list