[Equest-users] Equest Cooling Towers
David Eldridge
DEldridge at grummanbutkus.com
Wed Nov 20 09:43:27 PST 2013
If the chillers are running, the towers must also be running or else the condenser water would be getting very warm! As John A mentioned your files would help, or at least let us know which of the outputs makes you think the towers are not operating, or screen shots of the cooling tower dialog box.
One possible scenario is that you have some combination of high condenser water setpoint (causes towers to run less than if the water temperature is reset to a lower value) and efficient tower fans (kW/cell may be too low). The kW/cell in particular could be entered incorrectly, allowing your tower to run while not accumulating many kWh of end-use.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Gabriel M. Martinez
Sent: Wednesday, November 20, 2013 10:46 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Equest Cooling Towers
Hi, newbie eQuest user. I have modeled a fairly straight-forward loop that consists of multiple chillers and cooling towers. However, when I run the model, the chillers are running as they should but the cooling towers are not running at all, all year round. I tried running it with and without a tower water loop pump, to no avail. The fans are on VFDs. Any suggestions?
Gabe Martinez
Mechanical Designer
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131120/5658b1b7/attachment-0002.htm>
More information about the Equest-users
mailing list