[Equest-users] DD wizard HVAC system type issues

Jesse Henson jhenson at oculus-studio.com
Wed Oct 2 17:22:28 PDT 2013


Equest Users,

Has anyone encountered the following problem?

DD wizard incorrectly assigns the return path to "DUCTED" for "PACKAGED DX
PARALLEL FAN-POWERED VAV W/ ELEC REHEAT".

We discovered this problem after only changing "RETURN AIR PATH" from
default "DUCTED" to "PLENUM" and then reviewing the SS-J report to find the
SQFT/Ton is 2x what it should be (968 ducted vs. 526 plenum).

Please let me know your feedback ASAP.

Best, Jesse

-- 
Jesse Wolf Corsi Henson AIA, NCARB, LEED AP

*Oculus Studio*
275 N. Gateway Drive, suite 130
Phoenix, AZ, USA 85034
602.430.4264

http://www.oculus-studio.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131002/d55c39a7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: hvac system type.pdf
Type: application/pdf
Size: 387258 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131002/d55c39a7/attachment.pdf>


More information about the Equest-users mailing list