[Equest-users] ASHRAE 90.1 Baseline generalization

Paul Erickson perickson at aeieng.com
Fri Sep 13 09:49:41 PDT 2013


Ryan,

I'd second Stormy's suggestion of looking at the PNNL models, just note that some, such as the healthcare model, are simplified and may not fully characterize more typical 90.1 modeling results.  You will likely see that systems will range in performance based on type of building.  Also, as you may already appreciate, climate zone plays a huge role.  The same lab or hospital model in Seattle, Chicago, and Miami can easily range in performance from 50-500 kBtu/sf-yr depending on types of systems and ventilation requirements.

Paul

Paul Erickson  LEED(r)BD+C
Practice leader Sustainable



AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Boulevard | Madison, WI  53719

P: 608.236.1112 | C: 303.859.7523
perickson at aeieng.com<mailto:perickson at aeieng.com>  |  www.aeieng.com<http://www.aeieng.com/>


From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Stormy L. Shanks
Sent: Friday, September 13, 2013 11:33 AM
To: Bishop, Bill; Ryan Black; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ASHRAE 90.1 Baseline generalization

Ryan,

I don't disagree with you or Bill that this is hard to pin down, and the effort probably wouldn't result in extremely valuable results. But, here's a link to a collection of 90.1 prototype building models and scorecards created by PNNL: http://www.energycodes.gov/development/commercial/90.1_models. Maybe it would help you gain a better intuition about the EUI for different types of 90.1 baseline buildings.

Stormy

[cid:image001.png at 01CE0924.38506AB0]

Stormy L. Shanks, PE
Mechanical Engineer

2882 106th St, Des Moines, IA 50322




From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Friday, September 13, 2013 11:00 AM
To: Ryan Black; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] ASHRAE 90.1 Baseline generalization

Ryan,
I drive a 2005 Civic Hybrid, 5-spd manual. My boss drives an Audi A4 1.8t. How much gas do we each use per year?
Yes, you are right in your thinking.

Regards,
Bill

William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114            F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>           www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P   Sustainability - the forest AND the trees. P

From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ryan Black
Sent: Friday, September 13, 2013 10:47 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] ASHRAE 90.1 Baseline generalization

This isn't so much an eQuest question, as an ASHRAE 90.1 Baseline question. I have been tasked with producing a general Btu/sq ft or kWh/sq ft for an ASHRAE 90.1-2007 Baseline building for the given system types. My thought is that this is not really possible to nail down to one number or even an accurate range, as it depends heavily on building usage type. Scheduling and occupancy are going to affect equipment capacities, ventilation rates (and thus heating and cooling), and overall energy usage. Am I right in my thinking, or is there a way to get around building type to get that flat energy/sq ft for the different systems?

Any input would be greatly appreciated! Thanks!

Ryan

________________________________
This message and any attachments contain information intended for a specific party and may include sensitive or confidential material. If you are not the intended recipient, please do not read, copy, use, or disclose to others. Please notify the sender of the delivery error by reply and then permanently delete this message and all attachments.
  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130913/4cc041a0/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 9229 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20130913/4cc041a0/attachment-0002.png>


More information about the Equest-users mailing list