Ok here goes - copying the group in case anyone else has better feedback
At first glance here's a couple of impression. I don't do too many single family homes, so my mental validation might be off.
* The fan load is high compared to everything else. Partly because everything else is really low. Your annual EUI is 13.2 KBTU/ft2-yr - that's very low - even for a house. This makes sense with a GSHP.
* 1" static pressure on your fans might be high for a residential terminal unit that's not ducted.
* PVVT might not be the best system choice to go with a ground loop - try a water loop heat pump. You will still have fan energy, but with a terminal unit (as opposed to a ducted one) you should see that go down.
* The heat recovery system for the ventilator is a more complex matter that will require you to go well beyond the SD wizard. You will need to model a DOAS with energy recovery.
Vikram Sami
Associate Partner
ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com
925 Fourth Avenue, Suite 2400
Seattle, WA 98104
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Tuesday, September 17, 2013 3:17 PM
To: James Mathias; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] One question about eQUEST
James,
What is your system selection? Also - could you attach your inp file?
Vikram Sami
Associate Partner
ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com<mailto:vikram.sami at zgf.com>
925 Fourth Avenue, Suite 2400
Seattle, WA 98104
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James Mathias
Sent: Monday, September 16, 2013 3:04 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] One question about eQUEST
Hello,
I have one, I think fairly simple questions about eQUEST.
1. My simulation shows quite a bit of energy used by ventilation fans but it is for a simulation of a house that does not have ventilation fans. Where can I tell eQUEST there are no ventilation fans? I do actually have an heat recovery ventilation system but it runs for about only 2 hours each day. Does eQUEST have the ability to simulate that also?
James Mathias, Ph.D., P.E.
Associate Professor
Mechanical Engineering and Energy Processes
Mailcode 6603
ENGR E-024, 1230 Lincoln Drive
Carbondale, IL 62901
618-453-7016, -7658 fax
--
This message has been scanned for viruses and
dangerous content by MailScanner<http://www.mailscanner.info/>, and is
believed to be clean.
________________________________
The contents of this email and any attachments to it contain confidential and/or legally privileged information from Zimmer Gunsul Frasca Architects LLP or its affiliates. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, be aware that any disclosure, copying, distribution, or use of the information contained herein is strictly prohibited. If you received this transmission in error, please contact the sender and destroy the material in its entirety, whether in electronic or hard copy format.
________________________________
The contents of this email and any attachments to it contain confidential and/or legally privileged information from Zimmer Gunsul Frasca Architects LLP or its affiliates. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, be aware that any disclosure, copying, distribution, or use of the information contained herein is strictly prohibited. If you received this transmission in error, please contact the sender and destroy the material in its entirety, whether in electronic or hard copy format.