[Equest-users] Modeling GLHP systems

behnam jowkar behnamjowkar at gmail.com
Mon Apr 7 11:29:44 PDT 2014


Dear All:

I am trying to model a ground loop heat pump system in equest, but I keep
getting the following errors: " WLHP loop: Ground Loop has exceeded a
hi/low alarm limit and will shut down associated HVAC equipment for the
hour. Loop T:  17.91  Limit:  20.00. Verify that alarm limits are
reasonable, verify primary equipment sizing, especially ground-loop
heat-exchangers, and verify that the HP performance curves are suitable for
the intended operating range." as well as "Ground-loop HX: Ground Loop Heat
Exchanger 1 is undersized for the load and is producing an extreme
temperature of -4F."

Since the design is a closed loop system (vertical pipes) I have created a
GLHE of type 'Vertical Well-Sweden G-function', connected to a circulation
loop of the type 'water loop heat pump'. I have also inserted the GSHP
curves from DOE 22. I'm not sure if the problem is the parameters I have
defined in the model, or from the way I have set things up in EQUEST. I
would really appreciate it if someone with more experience than me can help
me out with my problem. I have attached my files in case someone has the
time to take a look at them.

Best Regards,

Behnam

-- 
Behnam Jowkar, MASc, BEng, LEED GA
Mechanical Engineer In Training
p: 416-716-5758
e: behnamjowkar at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140407/f728659a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 650-Brock Ave-Proposed.pd2
Type: application/octet-stream
Size: 183713 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140407/f728659a/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 650-Brock Ave-Proposed.inp
Type: application/octet-stream
Size: 554830 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140407/f728659a/attachment-0001.obj>


More information about the Equest-users mailing list