[Equest-users] PERFORM-DATA-AC Error
A Ramirez Zarzosa
aramirez at zeta3.com
Tue Dec 9 01:27:48 PST 2014
Thank you Christopher,
The FOCS WATER 7240 Capacity is 1906 Kw, which is 6,5 MBtu/h, yes it was a units coma error converting units. Cleaning all of them the problem persists.
Best Regards,
Aurelio Ramirez
Z3
From: Jones, Christopher [mailto:cjones at halsall.com]
Sent: lunes, 08 de diciembre de 2014 16:17
To: A Ramirez Zarzosa; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] PERFORM-DATA-AC Error
You will also find that the capacities for the chillers and boilers are too high. For example, Chiller 2A FOCS WATER 7240, capacity = 6503.5. BDL reports CAUTION, Value greater than the maximum of 100. Note, 6503.5 means 6503.5 million BTU/hr, 541,960 tons!
Christopher Jones, P.Eng.
Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nicholas Caton
Sent: Monday, December 08, 2014 9:26 AM
To: A Ramirez Zarzosa; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] PERFORM-DATA-AC Error
Do you have an .inp of a recent, stable (at least completing simulation attempts) iteration for the same project prior to exhibiting these errors? It may prove fruitful to compare against the most recent version.
The text & position of the referenced chiller BDL errors specifically suggest something awry with the retrieval of the library screwH20 curves… However perhaps more importantly I observe the eQuest interface is not behaving normally (for example, neither chiller accepts a CW loop assignment), and even when the offending chillers are removed, a large number (100’s) of new bdl errors occur concerning missing system inputs (which exist), building shades, and zone HVAC inputs appear…
My gut tells me the sheer size of this model is a primary factor – appears to be a full campus of buildings. The chillers and associated inputs may not be the true source of this instability. It might prove fruitful to break the model up into smaller portions.
~Nick
NICK CATON, P.E.
Owner
Caton Energy Consulting
1150 N. 192nd St., #4-202
Shoreline, WA 98133
office: 785.410.3317
www.catonenergy.com
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of A Ramirez Zarzosa
Sent: Monday, December 08, 2014 2:23 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] PERFORM-DATA-AC Error
Hi Guys,
I have two screw chillers, with water cooled condensers. In the Chiller properties, in both of them in the “Condenser type” box: is written “water cooled”. When I try to run the simulation. Two errors arise that does not allow me to perform the simulation.
2 error(s) found in project’s BDL input file.
_____
BDL. Input/Underline:
0.00975338, -0.00005891, -0.00458177) --
BDL Error:
PERFORM-DATA-AC in Chiller 2A FOCS WATER 7240 has Expression Evaluation Error: BDL Symbol ‘AIR COOLED” not found.
_____
BDL. Input/Underline:
--
BDL Error:
PERFORM-DATA-AC in Chiller 3A FOCS WATER 7240 has Expression Evaluation Error: BDL Symbol ‘AIR COOLED” not found.
_____
I would be glad if you advice me on how to solve this problem.
Many Thanks in advance.
Best Regards,
Aurelio Ramírez Zarzosa
Ingeniero de Caminos, Canales y Puertos
Z3
Avenida de Europa, 14
Parque Empresarial La Moraleja
28108 - Alcobendas
Madrid, (Spain)
cid:image002.png at 01CD8041.A3A93F60
tel.+34 911 890 523
fax.+34 917 660 444
e-mail. aramirez at zeta3.com
Viste nuestra pagina/Visit our - web: <http://www.zeta3.com/> www.zeta3.com
www.segoviaacueducto.com <http://www.segoviaacueducto.com/>
www.casaagua.com <http://www.casaagua.com/>
cid:image005.png at 01CD8041.A3A93F60
Miembro Fundador del/Founding Member: Consejo Construcción Vede España (Spain Green Building Council) desde/since 1998. <http://www.spaingbc.org/> www.spaingbc.org
USGBC Docs1410
Miembro del/Member: U.S. Green Building Council desde el/since 2000. <http://www.usgbc.org/> www.usgbc.org
De acuerdo con la nueva ley Ley de Servicios de la Sociedad de la Información y Comercio Electrónico aprobada por el parlamento español y de la vigente Ley Orgánica 15 13/12/1999 de Protección de Datos española, le comunicamos que su dirección de Correo electrónico forma parte de un fichero automatizado que va dirigido a la lista de distribución de noticias de Z3, teniendo usted derecho de oposición, acceso, rectificación y cancelación de sus datos.
*Si desea que eliminemos sus datos de nuestra base, envíe un e mail con la palabra BAJA a <mailto:zeta3 at ciccp.es> zeta3 at ciccp.es
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141209/164657b4/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 2144 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141209/164657b4/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 10088 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141209/164657b4/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4219 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141209/164657b4/attachment.jpeg>
More information about the Equest-users
mailing list