[Equest-users] Water to water geothermal heat pump / Radiators / No cooling / Natural ventilation

Hall, Brendan BHall at karpinskieng.com
Fri Feb 7 08:13:14 PST 2014


A couple things to add:


-          There is also a heat pump chiller type that you can try, as opposed to zone WSHP  units. Either way make sure to get good performance data so you can generate custom performance curves, since the standard conditions for rating geothermal heat pumps are different than WSHP or air cooled heat pumps. There are some default curves in equest for WSHPs that are a good starting point though.



-          It is likely that the engineer ran GLHEPRO or some other sizing calculation on the geo loop so you may be able to get good ground temperatures from there.


-          With a two pipe loop it is always important to have the loop operation on a schedule or set to "Snap" to lock out cooling in the winter and vice versa.


-          System 9 and 10 are available in 2007 as a addendum.


-          In the non-cooled spaces I would check and see if there is still a minimum ventilation that needs to be maintained year round. Otherwise use the system 9 mentioned before, it is a hot water unit heater. It is easier and more realistic in my opinion than adding cooling where there is none.



Brendan Hall,  PE, LEED AP BD+C
Engineer, Mechanical
karpinski
ENGINEERING
3135 Euclid Avenue
Cleveland, OH  44115
P  216.391.3700<tel:216.391.3700> Ext 3111
E  bhall at karpinskieng.com<mailto:bhall at karpinskieng.com>
W www.karpinskieng.com<http://www.karpinskieng.com/>

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Friday, February 07, 2014 10:39 AM
To: Nick Patsos
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Water to water geothermal heat pump / Radiators / No cooling / Natural ventilation

Nick,
You could try running your model with water-to-air heat pump systems first (DX systems with water-cooled condensers), connected to a Water Loop HP loop with rejection to a Ground Loop HX of TYPE = HORIZ-SLINKY-LOOP (or whatever is appropriate for your closed-circuit loop, and sized per your actual design). A custom Hourly Report will give you the ground loop temperatures which you can then use to create the temperature schedule for the LAKE/WELL HX.
There is precedent for using the Systems 9/10 from 90.1-2010 for LEED. You can probably find the CIRs or other reference in the list archive.
~Bill

From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Patsos
Sent: Friday, February 07, 2014 10:23 AM
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Water to water geothermal heat pump / Radiators / No cooling / Natural ventilation

Bill thank you very much, I will look into it with the approach you describe.

Regarding the temperature schedule for the GHX, is it possible to calculate it somehow? Sure there is limitation to the energy that the ground can receive from a closed circuit exchanger in comparison with the open loop that can receive any amount.

The project is for LEED for Schools 2009 so it uses the 90.1-2007, no heating only systems there.

Best regards

Nick Patsos
Mechanical Engineer


On 7 February 2014 16:53, Bishop, Bill <bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>> wrote:
Nick,
You can use a chiller of TYPE = HEAT-PUMP to model W2W GSHP. You attach it/them to a CHW loop of TYPE = PIPE2 (a two-pipe loop) that provides either hot or cold water but never at the same time, and configure the switchover using the Operation and Controls tabs of the loop. You can also add condensing boiler(s) to the two-pipe loop and stage them with the W2W chiller(s) using Equipment Controls and Load Management in the loop Controls tab. The GSHP connection to the ground loop is via a LAKE/WELL CW loop, to which you can attach a GROUND-LOOP-HX of TYPE = LAKE/WELL. You have to specify the temperatures of the HX in the LOOP-TEMP-SCH (they are not calculated hourly like they are for the other GHX types) or eQUEST will default to the monthly ground temperatures from the weather file.
I would look into the heating-only Systems 9/10 in 90.1-2010 for spaces with no cooling.
Regards,
Bill

William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[webCertified_logo_colorRGB72DPI.jpg]



134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 698-1956                        F: (585) 325-6005

bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>             www.pathfinder-ea.com<http://www.pathfinder-ea.com/>

[earth for signature]Sustainability - the forest AND the trees.


From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Nick Patsos
Sent: Friday, February 07, 2014 7:00 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Water to water geothermal heat pump / Radiators / No cooling / Natural ventilation

Hello all,

I need your opinions on a very complex system that I have to model for LEED in eQuest.

The system is a water to water geothermal heat pump capable of producing hot water for heating and in the summer season chilled water for cooling, not simultaneously.

The hot water is to be used by low-temp radiators (no fans) in spaces or FCUs. In some spaces ERV ventilators provide fresh air (constant speed) / in some only natural ventilation is provided (significant issues there to be discussed in due time).

There are spaces which have no heating/cooling by FCUs, only radiators (with ERVs or without).

I have made a diagram to give a quick overview picture attached.

The issues are as follows:

1) I tried modelling a Loop-to-loop heat pump system producing both hot and chilled water but I find significant consumption in cooling (coincident with heating) in the winter months which is highly unusual, thus very increased overall consumption in comparison with the baseline packaged VAV (PVAVS) system. Any alternatives ?

2) For the not cooled spaces I used baseboard heating and as system PVAVS cooling (due to the same as baseline cooling condition), I don't know if this is the correct approach. For the fan power of PVAVS do I have to use the same as baseline kW/cfm ? What about when the system is in heating when only baseboards should work (no fans) ? How 's this to be modeled ? Any ideas?

3) For the geothermal loop, I have a ground loop heat exchanger, now modelled as Lake/Well (due to limitations of the Loop to Loop heat pump) but in reality it will be a straight pipe closed circuit loop. I remember reading about creating a custom temp. schedule to model the exchanger, is it possible ?

4) Something more obvious than the above but still unsure, is PVAVS in eQuest the way to model Packaged VAV with Reheat as in 90.1 ?

5) Has anyone successfully tried the Shermad-Grimsrud method for natural ventilation in eQuest ?

As you see, it is really messed up, mostly due to the water-to-water heat pump. I know that I'm asking lots of questions in different topics at once. Ideas in any of the topics are greatly appreciated.

Nikos Patsos
Mechanical Engineer

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140207/f3c58b94/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140207/f3c58b94/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 4600 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140207/f3c58b94/attachment-0002.png>


More information about the Equest-users mailing list