[Equest-users] HVAC system definition
Nick Caton
ncaton at smithboucher.com
Mon Feb 10 15:29:08 PST 2014
Vladimir/Frantisek:
I haven't done a 2-pipe system in eQuest for some time, but to my recollection the actual "Fan Coil" (FC) system is pretty limited in that you can model a ventilation component (and preheat), but not a central fan or pre-cooling. It's very much a self-contained system.
Here's a stab toying around with a dummy model:
2-pipe fan coil systems are not an option in the wizards, but I believe you can start by selecting 4-pipe fan coils there, then changing the associated hydronic loops /assignments to be a 2-pipe loop (pay careful mind to the 2-pipe loop operation inputs):
[cid:image003.png at 01CF2684.951ABDD0]
>From there, I think you could approximate the system you're describing by switching your airside systems to Induction Unit:
[cid:image004.png at 01CF2685.51D93910]
With this setup, you'll likely need to make adjustments to your terminal units (as defined at the zones) to behave like your actual fancoil units with respect to fan control and so forth.... But a quick simulation of what I just threw together per the above screengrabs simulates without substantial unmet hours or errors.
Hope that helps you both move forward!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: Vladimír Svozil [mailto:svozil at enerfis.cz]
Sent: Monday, February 10, 2014 2:56 PM
To: equest-users at lists.onebuilding.org; John Kopf; Nick Caton
Subject: Re: [Equest-users] HVAC system definition
Hello there,
i am collegue of Frantisek working on the same issue. The system that is designed by design team is AHU with heat/cool coils and then just 2-pipe FCU as a secondary cooling for offices. And baseboards/radiators for primary heating. I don't see a problem with baseboards because we can combine them togather with 4-pipe FC, VAV etc. The problem for us is how to combine 2-pipe secondary cooling FC togather with ventilation system (AHU).
The strategy of creating narrow perimetr zone sounds interesting but i dont see a problem with baseboards at this moment.
Thanks for advices a Hezký večer do Kanady,
Vladimir
Dne 10.2.2014 19:35, Nick Caton napsal(a):
Further to that last point, I've often defined relatively narrow perimeter zones specifically to account for perimeter baseboard heaters. If you pursue this strategy, I suggest being very careful to define appropriate interior air walls with the adjacent interior spaces to aid in heat transfer, and/or else re-appropriate some of the interior loads of the core areas to the perimeter zones, to avoid erroneous unmet heating hours from those zones.
Best regards,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Kopf
Sent: Monday, February 10, 2014 12:12 PM
To: František Bartoš
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] HVAC system definition
Dobry Den Frantisek,
Nazdar z Kanady! Na co používáte eQUEST v České republice? Budu pokračovat v angličtině...
For items 1 & 3, one of the HVAC systems available is fan-coil. This will allow for both a central AHU with your pre-heat and pre-cool. In wizard mode, you can select 4-pipe fan coil by setting the cooling source to chilled water coils and heating source to hot water coils (and can tweak this later in detailed mode if necessary).
For the baseboards, you can turn on baseboards for zone heating in wizard HVAC screen 6, though I don't think these account for the fan energy.
Another option would be to split up your zone and select unit heaters for those areas (e.g. stairwells, vestibules) if you can split it up like that.
Regards,
John
John Kopf, BEng, MASc, EIT, LEED AP BD+C
Sustainability Analyst
Stantec
200 - 325 25th Street SE Calgary AB T2A 7H8
Phone: (403) 716-8006<tel:%28403%29%20716-8006>
Fax: (403) 716-8049<tel:%28403%29%20716-8049>
John.Kopf at stantec.com<mailto:John.Kopf at stantec.com>
On Mon, Feb 10, 2014 at 8:54 AM, František Bartoš <bartos at enerfis.cz<mailto:bartos at enerfis.cz>> wrote:
Hi,
I am modeling standard office building in equest v3.65 and I have trouble with choosing the HVAC system type. Our designed HVAC system is following:
1) Central AHU with preheat/precooling chamber of outdoor air
2) Local baseboards for secondary heating (only circulation of indoor air)
3) FC units for secondary (only circulation of indoor air)
All these are for 1 zone. My question is - how to model this as equest allows only 1 HVAC system per zone?
Thanks for advice.
Frantisek
--
František Bartoš
Energetika a certifikace budov
Enerfis s.r.o.
Tel.: +420 222 766 952<tel:%2B420%20222%20766%20952>
Fax: +420 222 766 959<tel:%2B420%20222%20766%20959>
Mob: +420 607 965 265<tel:%2B420%20607%20965%20265>
E-mail: bartos at enerfis.cz<mailto:bartos at enerfis.cz>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140210/35198474/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140210/35198474/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 10560 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140210/35198474/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 19492 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140210/35198474/attachment-0005.png>
More information about the Equest-users
mailing list