[Equest-users] ERV equivalent in baseline model?
Tianyao Zhang
tinazhang0330 at gmail.com
Sat Feb 22 22:47:01 PST 2014
Nathan,
Thanks for the clarification - I am using the Energy Star Multifamily High
Rise Guidelines and it does seem like the units are hybrid and I would need
to change the baseline system type to PTAC. I just found that the common
errors for primary system type listed in Advanced Energy Modeling for LEED
Technical Manual v2 include "Baseline HVAC system is mapped using "Electric
and Other" heating source classification when fossil fuel is used in
conjunction with electricity to heat spaces in proposed case (the heating
type should be hybrid)", and "Heating source of proposed case with fossil
fuel preheat is not treated as hybrid if heating source of rest of building
is electricity.", which I believe is the error I'm making.
Thanks,
Tianyao
2014-02-21 17:33 GMT-05:00 Nathan Miller <nathanm at rushingco.com>:
> Is this a project using the LEED for Homes Midrise protocol with the
> ENERGY STAR Multifamily High Rise Simulation Guidelines? If so, it is worth
> noting that while you are (probably) grand fathered in with whichever
> version of the ESMFHR Sim Guidelines that were in place when the project
> registered for LEED, you also have the option of using the more updated
> versions.
>
>
>
> *We've found that the latest release (dated Sept 2013) contains
> significantly more detail on how to select the baseline system than the
> previous versions. I don't entirely agree with the rationale in this
> document (I think there is some twisting of the 90.1 language), but at
> least it tries to sort things out. I *think* you would fall under the
> example 3 in the below excerpt? *
>
>
>
> Link:
> http://www.energystar.gov/ia/partners/bldrs_lenders_raters/downloads/mfhr/ENERGY_STAR_MFHR_Simulation_Guidelines_Version_1.0_Rev02.pdf
>
>
>
> Some Key Excerpts:
>
> 3.8 HVAC
>
> 3.8.1 Every space that is modeled as cooled in the Proposed Design
> simulation shall also be modeled as cooled in the Baseline Building
> Design. Likewise, every space that is modeled as heated in the Proposed
> Design simulation shall also be modeled as heated in the Baseline Building
> Design. Unconditioned and semi-heated spaces shall also match between the
> Proposed Design simulation and Baseline Building Design.
>
>
>
> a. Model the entire living (including all dwelling unit) space, as well as
> offices, community rooms and other conditioned spaces, except as described
> below, as heated and cooled.
>
> b. Do not model cooling in corridors and utility spaces such as
> mechanical rooms, laundry rooms, etc. unless the spaces are cooled in the
> Proposed Design. Per addendum dn to ASHRAE 90.1-2007, such thermal zones
> shall be modeled using constant volume Heating and Ventilation systems in
> the Baseline Building Design. The heating source shall be warm-air furnace,
> gas-fired, if the building's predominant heating source is Fossil Fuel,
> Fossil/Electric Hybrid, or Purchased Heat, and warm-air furnace, electric
> resistance in other cases. System design supply airflow rates for these
> baseline systems shall be based on the temperature difference between a
> supply air temperature setpoint of 105°F and the design space heating
> temperature setpoint; the minimum outdoor air flow rate; or the air flow
> rate required to comply with applicable codes or accreditation standards,
> whichever is greater. Each thermal block shall be modeled with a separate
> HVAC system and the following baseline fan power:
>
> Pfan,supply = CFMs * 0.3.
>
> Pfan,supply electric power to supply fan motor (watts)
>
> CFMs the baseline system maximum design supply fan airflow rate in
> cfm
>
> 3.8.2 The Baseline and Proposed HVAC system shall be modeled as per
> Appendix G, and as clarified in the first note below Appendix G Table
> G3.1.1A, "...Residential building types include dormitory, hotel, motel, and
> multifamily." Following this note, common spaces that are essential to the
> building's residential function, including but not limited to corridors and
> stairwells, must be modeled with residential baseline HVAC system type
> (System 1 or 2 only) depending on the predominant fuel source in the
> building, except as allowed in 3.8.1. Appendix G exception G3.1.1(a) that
> allows the use of additional system types for nonpredominant conditions if
> they total more than 20,000 ft2, only applies to heating source, not space
> function. Baseline HVAC System Types 3-8 may not be used, except in
> appropriate nonresidential spaces that exceed 20,000 ft2.
>
>
>
> *Example 1:* 25 story multifamily building heated predominantly with gas
> has 1,000 ft2 of common space on each floor, including corridors, trash
> rooms, and stairwells. Together, these spaces account for 25,000 ft2.
> Corridors are heated with gas and cooled. Stairs are heated with electric
> resistance but not cooled. What baseline system type should be modeled for
> the common spaces?
> *Correct Approach:* Apartments and corridors are modeled with Baseline
> HVAC System 1-PTAC. Stairs that are heated but not cooled are modeled with
> Heating and Ventilation System as described in 3.8.1, which results in
> Baseline HVAC System 11, not 10.
>
> *Incorrect Approach:* Common spaces are modeled with baseline System 7
> following exception G3.1.1(a), since they account for over 20,000 ft2 and
> cover more than 5
>
> floors.
>
>
>
> *Example 2:* 25 story multifamily building heated predominantly with
> electricity has 1,000 ft2 of common space on each floor, including
> corridors, trash rooms, and stairwells. Together, these spaces account for
> 25,000 ft2. Corridors are heated with gas and cooled, and account for
> 21,000 ft2. Stairs are heated with electric resistance but not cooled. What
> baseline system type should be modeled for the common spaces?
>
> *Correct Approach:* Apartments are modeled with Baseline HVAC System
> 2-PTHP. Stairs that are heated but not cooled are modeled with Heating and
> Ventilation System
>
> as described in 3.8.1, which results in Baseline HVAC System 10 since the
> building's predominant heating source is electric. Corridors can use
> Appendix G exception G3.1.1(a) in order to model Baseline HVAC System
> 1-PTAC in the corridors of the Baseline Building Design.
>
>
>
> *Example 3:* 25 story multifamily building with electric heat pumps
> serving the apartments and corridors are heated with gas, but provide
> ventilation directly to the apartments. What baseline system type should be
> modeled for the apartments?
> *Correct Approach:* This qualifies as fossil/electric hybrid and
> therefore apartments and corridors are modeled with Baseline HVAC System
> 1-PTAC.
>
>
>
> *Nathan Miller **-* *PE, LEED(R)AP BD+C, CEM*
>
> *Mechanical Engineer/Senior Energy Analyst *
>
> *RUSHING* | *D* 206-788-4577 | *O* 206-285-7100
>
> *www.rushingco.com <http://www.rushingco.com/>*
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Tianyao Zhang
> *Sent:* Friday, February 21, 2014 2:14 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] ERV equivalent in baseline model?
>
>
>
> Hi all,
>
>
>
> I'm modeling a LEED for Homes building, the proposed design uses Variable
> Refrigerant Flow systems with a rooftop Energy Recovery Unit providing 100%
> OA, everything is electric except the ERV unit, which uses natural gas. My
> baseline model system type is PTHP. My question is, since the proposed case
> has natural gas as one of its heating source, does the baseline case
> systems have to be revised to include natural gas as well? The problem is
> there isn't an ERV equivalent in the baseline model, so I'm not sure where
> to add the natural gas units, if necessary.
>
>
>
> I appreciate any feedback on this matter, thank you!
>
>
>
> --
>
> Tianyao Zhang
>
>
>
> M.S. Graduate in Architecture - High Performance Buildings
>
> College of Architecture
>
> Georgia Institute of Technology
>
> Atlanta, GA
>
> 404-834-0120
>
>
>
--
Tianyao Zhang
M.S. Graduate in Architecture - High Performance Buildings
College of Architecture
Georgia Institute of Technology
Atlanta, GA
404-834-0120
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140223/77f82626/attachment-0001.htm>
More information about the Equest-users
mailing list