[Equest-users] Modeling District Energy Systems for LEED
Scott Parker
sparker at aeieng.com
Mon Jan 6 08:42:41 PST 2014
Omar,
For the "modeling" option you will need to model the plant with the assumed full load (which includes more than just the one building). In a separate energy mode: Run an energy model with load from all buildings on it, and then use the average efficiency (e.g. kW/ton, COP, etc) in the building model as a constant efficiency for the whole year.
For example, from the plant model you may come up with a COP = 5.1 as an annual average. Then the building model would use COP = 5.1 as a constant value.
I'll leave it up to you to determine the best way to model the full load on the DES plant, but this could be estimated with a relatively simple model. The modeling software Trace has a specific feature for this, but you can manually do this in eQuest with a little work.
Regards,
Scott
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar Katanani
Sent: Monday, January 06, 2014 11:30 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling District Energy Systems for LEED
Dear Sirs,
I am modeling a school building for LEED which has a Campus Energy System (water cooled chiller and diesel boiler). The DES was installed almost 8 months ago for the first phase of the project.
Now, I am modeling for the project's second phase, and additional chillers / boilers will be added to the DES in order to be able to serve both phases in addition to any potential building on campus in the future.
1) Looking at the USGBC's guidance for DES (Appendix C): in order to determine the proposed building heating / cooling efficiency, I guess I have to go with the "Modeling" option because the DES will be expanded as part of my project (so it's not existing).
For this option, do I have to create a separate model of the district plant, or shall I add this district plant to my project's model? Appendix C says "Apply measured or estimated load profiles as "process loads" to reflect the estimated total loads on the plant". If this is the case, then if I add the process loads in addition to my project's loads, I will be double counting the loads, right?
Does this mean I have to create a dummy project building (with no loads) with the proposed district plant to determine the efficiencies?
2) Does anyone have additional guidance for modeling district energy systems, other than the one of the USGBC? Something with more examples or maybe a case study with actual numbers?
Best regards,
Omar
___________________________
Omar Katanani
Senior Sustainability Engineer
Email: omar at ecoconsulting.net<mailto:omar at ecoconsulting.net>
EcoConsulting (Lebanon)
Nahas Building, 4th floor
Georges Haddad Avenue
Postal Code: 2028 5806, Saifi District
Beirut, Lebanon
Tel: +961 (0) 1 971 266
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 20 8144 0015
Website: www.ecoconsulting.net<http://www.ecoconsulting.net/>
[Description: EcoConsulting Membership Logos (low res)]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140106/1759a3bc/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 7393 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140106/1759a3bc/attachment-0002.jpg>
More information about the Equest-users
mailing list