[Equest-users] I need to get help to "Cooling Setpoint Control: OA Reset" (urgent)!
Jeon, MiYoung
MiYoung.Jeon at tetratech.com
Tue Jan 14 18:28:50 PST 2014
Energy saving from OA-reset control depends on the design values and weather data.
If you model OA-reset control, electric consumption for the space cool, heat rejection and pump & fan will be reduced.
I just ran a test to inform you the effects of OA-reset and as a result, an electric consumption saving is 2 %.
This is just one of various cases. In order to get a precise result, you should predict the saving using the hourly report and weather data as well.
Thank you.
Miyoung Jeon LEED AP BD+C| Modeling Engineer
Direct: +82.2.2051.5097 | Fax: +82.070.4170.4101 | mjeon at cosentini.com<mailto:mjeon at cosentini.com>
Tetra Tech International Korea Inc. | Cosentini
3F Dongyoung Bldg. 891-62 Daechi4-Dong Gangnam-Gu | Seoul, Korea 135-840 | http://www.cosentini.com/korea.html
From: 허정숙 [mailto:jasmine.hue at lge.com]
Sent: Wednesday, January 15, 2014 10:23 AM
To: Jeon, MiYoung; equest-users at lists.onebuilding.org
Subject: 회신: [Equest-users] I need to get help to "Cooling Setpoint Control: OA Reset" (urgent)!
Thanks for your reply
I already tried this but my problem is not that the result is not much of what I expected.. not much saving from this OA rest control. I am wondering if I did it in a correct way
보낸 사람: Jeon, MiYoung [mailto:MiYoung.Jeon at tetratech.com]
보낸 날짜: Wednesday, January 15, 2014 9:58 AM
받는 사람: 허정숙; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
제목: RE: [Equest-users] I need to get help to "Cooling Setpoint Control: OA Reset" (urgent)!
Dear Jasmine,
You can model ‘OA Reset Set-point control’ using chilled water loop’s controls.
There are four control sequences. (Fixed, OA-reset, Scheduled, Load-reset)
See the picture below. If you need help, feel free to contact me.
Thank you.
[cid:image003.jpg at 01CF11D7.535D0680]
Miyoung Jeon LEED AP BD+C| Modeling Engineer
Direct: +82.2.2051.5097 | Fax: +82.070.4170.4101 | mjeon at cosentini.com<mailto:mjeon at cosentini.com>
Tetra Tech International Korea Inc. | Cosentini
3F Dongyoung Bldg. 891-62 Daechi4-Dong Gangnam-Gu | Seoul, Korea 135-840 | http://www.cosentini.com/korea.html
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of 허정숙
Sent: Wednesday, January 15, 2014 8:26 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] I need to get help to "Cooling Setpoint Control: OA Reset" (urgent)!
Dear eQuest expert,
Is there anyone who have experienced with modeling the chilled water supply reset according to “OA Reset Set-point control” in Cooling? In other words, chilled water supply temperature will be changeable according to OA temperature (Lower OA temp, high chilled water supply temp). Can you help me out on how to set up the model in order for this to be working successfully.
I really need to model this as accurate as possible. Your help would be greatly appreciative. Thanks so much for your help in advance. Cheers
허정숙 과장 (Jasmine Hue), LEED AP, CEM
Manager, BdMS Product Planning Group
BdMS Business Unit/ AE/ LGE
jasmine.hue at lge.com<mailto:jasmine.hue at lge.com>
M: (+82)-10-3576-6194
T: (+82)-2-3777-2896
[보안문구]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140115/93d0321f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 25864 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140115/93d0321f/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 96300 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140115/93d0321f/attachment-0005.jpg>
More information about the Equest-users
mailing list