[Equest-users] Baseline Fan power calculation
Hala Jaber
halajaber82 at gmail.com
Wed Jan 22 13:24:17 PST 2014
Thanks steven, but the indoor design thermostat temperature 22C , which is
not exaggerated ,since my building is office building and the recommended
design temp is 22C as per ASHRAE guidlines,the design throttling range in
my design is 0.83 K(Kelvin),so does it make it realistic?
On Wed, Jan 22, 2014 at 11:58 PM, Steve Tobin <stobin at smithboucher.com>wrote:
> From the outside looking in and not knowing your design requirements, I
> would question why your indoor “Cooling” thermostat temperature setpoint is
> set at 71.6 F? That seems like a low and extremely precise cooling
> setpoint to design to? Also what is your throttling range of your
> thermostat? Designing to something so precise would mean that our
> throttling range would be zero, which is not realistic.
>
>
>
> Also take a look at your AHU setup? Is it blow through or draw through,
> essentially where does your fan heat get included in the load, before or
> after the coil? If the system is draw through the cooling coil has to have
> a lower coil leaving air temperature to account for the added fan heat.
>
> Hope that helps.
>
>
>
> [image: cid:image001.jpg at 01CCA5C8.288E04E0]
>
> *Steven C. Tobin Jr., P.E.*
>
> PROJECT ENGINEER
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0061
>
> fax 913 345.0617
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Hala Jaber
>
> *Sent:* Wednesday, January 22, 2014 2:14 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Baseline Fan power calculation
>
>
>
> Hey eQuest users,
> I have a new challanging requirement in the appendix G section G3.1.2.8,
> its required the supply air-to room air cooling temperature difference is
> 20 degrees for each HVAC system. Now my question is how can i achieve this
> if my baseline is system 8 and the chilled water leaving temperature is
> specified 44 F with return delta t=12,at the same time that in my design
> the indoor thermostat temp=71.6 F , and the supply cooling temp should be
> 51.6F, here when i set this value i got an error in eQuest stating that"
> the cooling coil leaving temperatures must be at least 6 F higher than
> entering water temp" and when i set the cooling supply air temp below 55 F
> trying to achieve the 20 degree difference, i got this error.
> I hope if any one can help,who may face this in baseline model.
> Thanks.
>
> Hala Jaber
> Sustainablity Design Engineer.
>
--
Hala Jaber.
Sustainable Design Engineer.; LEED AP BD +C .
+962-79-7570197
email: halajaber82 at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140123/d4332345/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1778 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140123/d4332345/attachment-0002.jpeg>
More information about the Equest-users
mailing list