[Equest-users] Total Connected Lighting Load
Nick Caton
ncaton at smithboucher.com
Thu Jan 30 14:13:09 PST 2014
Very good point David - I think read too quickly and I put words in Daryll's mouth, so to speak...
My previous directions are specifically to determine a "connected" total as applicable for 90.1 LPD checks and similar exercises.
Maximum draw in actual operation is a potentially different thing. For that, I would direct you more simply to the PS-E reports, which list both coincident and non-coincident maximum draws by enduse.
This explains the difference faster than I could:
[cid:image004.png at 01CF1DD6.29D75B20]
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: David Eldridge [mailto:DEldridge at grummanbutkus.com]
Sent: Thursday, January 30, 2014 3:28 PM
To: Nick Caton; Kasun, Darryl
Subject: RE: Total Connected Lighting Load
Darryl - connected lighting load, or operating load based on the modeled (and potentially lower than as-built or in-operation) schedules?
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Thursday, January 30, 2014 3:22 PM
To: Kasun, Darryl; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Total Connected Lighting Load
Hi Darryl!
Two ideas come to mind to extract a connected total:
1. You could pull the W/SF figures for each space from the spreadsheet view and copy/paste into excel, then pull the areas for those spaces in the same order, then use excel algebra to multiply through and sum the results
2. Assuming you have only one unique lighting schedule (default for single shell wizard-borne projects), it may be quicker to create a separate fractional schedule that reflects 100% (1.00 per hour) operation all year. Swap that schedule in for the spaces, simulate, and observe the maximum lighting demand draw in the graphical reports.
There may well be a better/faster way - so keep your eye on the list, but I believe I've leveraged both of these approaches at one point or another.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kasun, Darryl
Sent: Thursday, January 30, 2014 1:36 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Total Connected Lighting Load
Good afternoon - I am trying to determine the total lighting load of the building I'm simulating. Is there a DOE-2 report that has this info or another keep method to get this info?
[cid:image002.jpg at 01CF1DD1.704B7F00]
Darryl Kasun, LEED(tm) AP BD+C | Mechanical E.I.T.
CBCL Limited 1489 Hollis Street PO Box 606, Halifax, NS B3J 2R7
T: 902-421-7241 x2522 | E: darrylk at cbcl.ca<mailto:darrylk at cbcl.ca> | F: 902-423-3938 |
W: www.cbcl.ca<http://www.cbcl.ca>
"Solving Today's Problems with Tomorrow in Mind"
[cid:image003.jpg at 01CF1DD1.704B7F00]
Please consider the environment before printing this e-mail. | S'il vous plait considérez l'environnement avant d'imprimer ce courriel.
Disclaimer<http://www.cbcl.ca/offmain/emaildisclaimer_e.html> | Désaveu<http://www.cbcl.ca/offmain/emaildisclaimer_f.html>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140130/80a0e715/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140130/80a0e715/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 8199 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140130/80a0e715/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 6728 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140130/80a0e715/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 169343 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140130/80a0e715/attachment-0002.png>
More information about the Equest-users
mailing list