[Equest-users] Can assign Zones to Middle Floors
Lee, Frank
Frank.Lee at baltimorecity.gov
Wed Jul 2 10:34:03 PDT 2014
Nick,
You are exactly right. I mixed up zones and activity Area Allocations.
Back on track.
Frank
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Wednesday, July 02, 2014 12:58 PM
To: John Aulbach; Lee, Frank; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Can assign Zones to Middle Floors
John/Frank:
I might be reading this wrong, but I think Frank may have actually unintentionally misled himself with his zone group naming scheme…
To make a clarifying distinction: “Zone groups” are not how floors are defined. They are merely ratios of space types, assigned to the geometrical spaces defined in previous DD wizard shell screens, with (optionally) zonal exhaust inputs (via the “zone group details…” button), and assignment to a specific HVAC system type (if you have more than one).
If I’m not mistaken, you have likely set up a 5-story building as a single shell, which means floors 2/3/4 are actually the same thing repeated 3 times. They can be differentiated after the wizards in detailed mode, if you do not tick the floor multiplier option in the first screen, but if you mean to utilize the wizard’s handy activity area allocation capacities to assign unique space allocations to each floor, you’ll need to make more than one shell (most directly, 1 shell per level).
As it stands, you can continue making unique zone group definitions (which simply assign a weighting of space types), but you could assign only three zone allocations at most, as it appears you only have 3 unique spaces (1 per floor). If you are okay with floors 2,3,4 sharing the same weighting of space allocations however, then you wouldn’t need to rethink your shell situation.
If you left-click on the middle floor space in the first screenshot you provided, do you get the context dialog to assign a defined zone group? You should be doing that for each space.
[cid:image005.png at 01CF95F9.456F4870]
Hope that’s helpful,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Wednesday, July 02, 2014 11:20 AM
To: Lee, Frank; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Can assign Zones to Middle Floors
Hi Frank:
I see you are in the DD Wizard, so you have the ability to assign those spaces to individual floors. However, you show only three floor plans and you are trying to name five. If you cut down the 2, 3, and 4 to say "Middle" you should be able to assign that Middle Zone to the middle floor plan.
See attached. BTW, I am using Version 3.64. If you installed 3.65, you can read it OK. I and others have some issues with the newer Version.
John R. Aulbach, PE
Los Angeles, CA
On Wednesday, July 2, 2014 9:09 AM, "Lee, Frank" <Frank.Lee at baltimorecity.gov<mailto:Frank.Lee at baltimorecity.gov>> wrote:
Another Newbe Question
I am creating my first model. DD Wizard Screen 14.
I’ve created the 2nd 3rd and 4th floor in a five story bldg. Can’t seem to assign them to the “Middle Above Grade” floor plan shown below.
No dialog box appears.
[cid:image007.png at 01CF95F9.456F4870]
Help says I should see this dialog box:
[cid:image008.png at 01CF95F9.456F4870]
Frank Lee
Facility Energy Auditor
Baltimore City Energy Office
Department of General Services
200 N. Holliday Street, Rm. 804
Baltimore, MD 21202
P: 410-396-1221
C: 410-627-8304
[cid:image009.png at 01CF95F9.456F4870]
Please click here to complete a customer service survey!<http://cp.mcafee.com/d/FZsSd1MQcz9J5yX3abRXFCXCQXTvKYZsQsCzASDuXZTDAmnzqtSm6nQjhOOqejqtNP2bzb5PhOrxrpRw2GaOCj8lrIj-fbCWaOCj8lrIj-fbCO2qbb11B_HYOCqenQn3hPRXBQQnxTfzzhOyUyqeumKDp5dmXzDaxVZicHs3jq9JMTvAm4TDNOb2pEVdTdw0GdNc-mlH0HVrBYFwc0o1wUov63vyPvQCnrFYq5O5mUm-wafBiteH3O3szQ9g8Y01dIEECzAsUr1vF6y0QJzgITZ9BSWv6xFtd40BI3h1Jai8Md404RxZ3h1eFEw6V887-q81s-JoQdLFCNP9vZFf0Ec1>
From: Jason Glazer [mailto:jglazer at gard.com]
Sent: Wednesday, July 02, 2014 11:59 AM
To: Lee, Frank
Subject: Re: List view for this list
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2014-July/date.html<http://cp.mcafee.com/d/k-Kr410q6jqb5S6knHTjdTdFTK_tVWVEVd79JeZTXLf8IL6QXIIcLECzBAQsCQXzC4n6mbCzAT2SPH05klBcCgGToDYundQlBcCgGToDYundA4Qmm23b_nVBcQsLEK6zDHTbFEL3Kv76zB5N4QsYJteOaqJT7el3PWApmU6CQPrxK_8I9LfzAm4PhOrKr01DOFeDlxV1KhW4E4u00UJ9rUyuubd_iptKDNEnH3O3szQ9g8Y01NeWb1s26POS8rf-1NLNpLWjbJQ-d2V2Hsbvg57OFeDlxV1KhW4E4u00CSkkjhOesdwLQzh0qmNEmr-AOXtfzgQKCy0iS1EwSB94o6y02qM-xEwDkQg3sA43_d40KvmIq6TQPoaePvviVlIjf>
but newest is on the bottom.
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2014-July/thread.html#start<http://cp.mcafee.com/d/5fHCNESyNtxB5WZQPtPqtXLTuuKqejhOrjLt-XPObbNJeXb3bW9EVpd79JeUVx5NByVEVdMJIWM1l5pj9AaJS9_7BPt5pj9AaJS9_7BPp1d5BwwO_R-pjd7bWbxEVWZOWqbMXDNNEVhshd7fbnjIyCHtNPBgY-F6lK1FJASUrLOb2rPUV5xcQsCXCM0pYGjFRougrAuxa17w0ebim-8DDyPvQCnrFYq5WMYwT8Z2k2f00sjKyMn0xIYJAOsvR3ws1B9X6pLNpLWjbJQ-d2V2Hsbvg57OFeDlxV1KhW4E4u00CSkkjhOesdwLQzh0qmNEmr-AOXtfzgQKCy0iS1EwSB94o6y02qM-xEwDkQg3sA43_d40KvmIq6TQPs__ozm4oEjeV>
by thread
On 7/2/2014 10:55 AM, Lee, Frank wrote:
Thanks Jason
Usually in a listgroup one can go the page with listing of current posts, newest on top, threads view…
Looks like these is not such a home page here. Correct?
Frank
From: Jason Glazer [mailto:jglazer at gard.com]
Sent: Wednesday, July 02, 2014 11:21 AM
To: Lee, Frank
Subject: Re: List view for this list
The archive is at:
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/<http://cp.mcafee.com/d/5fHCNEq6x0SyNtxB5WZQPtPqtXLTuuKqejhOrjLt-XPObbNJeXb3bW9EVpd79JeUVx5NByVEVdMJIWM1l5pj9AaJS9_7BPt5pj9AaJS9_7BPp1d5BwwO_R-pjd7bWbxEVWZOWqbMXDNNEVhshd7fbnjIyCHtNPBgY-F6lK1FJwSUrLOb2rPUV5xcQsCXCM0pYGjFRougrAuxa17w0ebim-8DDyPvQCnrFYq5WMYwT8Z2k2f00sd-bd_iptKDNEn8lrxrW0E-l9QWIf8dOfgB0zM04SOyyqehPxI5-Aq83iSd2PvQCnrFYq6BQQg2mMd46QF8z0Qg0jm7Qd44WCy0rAwwvVEw5PWRzgS-Cr38F5Xe8Nkzo1>
To post a new message, send an email to:
equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Let me know if you still have any questions.
Jason
On 7/1/2014 7:27 AM, Lee, Frank wrote:
Hi,
Just joined. Is there a page where current postings are listed? Or just Archive and the email to post?
I am accustomed to lists where current posts are posted.
Frank Lee
Facility Energy Auditor
Baltimore City Energy Office
Department of General Services
200 N. Holliday Street, Rm. 804
Baltimore, MD 21202
P: 410-396-1221
C: 410-627-8304
[cid:image009.png at 01CF95F9.456F4870]
Please click here to complete a customer service survey!<http://cp.mcafee.com/d/FZsS838ArhoKMOyZuWpKVJeZTXLfnd79EVdFTK_tVV5BUSDtBxBZ4QsICzASDssMyUONsQsCUmSto0GyIFAO5mX4_zOVKyIFAO5mX4_zOVIwCyOMgpvW_cFCzBZ5MQsZuVtd5UtPUUQsEK8CzDBHFShjlKUVOEuvkzaT0QS-rsdTV5xdVYsyMCqejtPo0azsjfBBqMa-mVvao3060oe67NwTUITZ9BSWv6xsxlK5LE2zVkDjGMYwT8Z2k2f00jraa9EV7e6MnWhEwdboQbd_iptKDNEqnjh09r0QgriAyc3h01dovgQgjGq81Ki21_Cy0nfHmd3rWpJ0h_p2Rp>
--
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
Admin for onebuilding.org building performance mailing lists
--
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
Admin for onebuilding.org building performance mailing lists
--
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
Admin for onebuilding.org building performance mailing lists
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<http://cp.mcafee.com/d/avndxNJ5yX3abRXFCXCQXTvKYZsQsCzASDuXZTDAmnzqtSm6nQjhOOqejqtNP2bzb5PhOrxrpRw2GaOCj8lrIj-fbCWaOCj8lrIj-fbCO2qbb11B_HYOCqenQn3hPRXBQQnxTfzzhOyUyqeumKDp5dmXzDaxVZicHs3jrxJMTvAm4TDNOb2pEVdTdw0PVkDjGMYwT8Z2k2f00sfBisEeRU1cYmr-AOXtfzgLm7A6V7EiwhU02rYmr-AOXtfzgKgGT2TQ1hYGjFRougrAuxa17w09JB54QszD3obZ8Qg6BIq5C_FcKTjUQdbFEw4Jwq8dFih61Ew0CIfEq89Rd40T910_Ph0bDRH6xJZcSa4Z8oZx>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140702/a53b6d70/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 28632 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140702/a53b6d70/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140702/a53b6d70/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 81151 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140702/a53b6d70/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 40611 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140702/a53b6d70/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 12502 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140702/a53b6d70/attachment-0003.png>
More information about the Equest-users
mailing list