You have the cooling control set at constant – do you know if the existing building has a sequence of operation to follow?
For a recent new building which had a VAV air handler with a chilled water coil (water delivered from an aquifer in this case, VFD drives, etc.) I used the below parameters, which appear to have a large effect on your model.
Travis
[cid:image003.png at 01CF9ABB.7D35BF70]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael Campbell
Sent: Tuesday, July 08, 2014 12:58 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] VAV System - high cooling energy in winter
Hi,
I’m trying to model an existing building with a chilled water VAV system. The chilled water usage is much higher in the winter time than expected. Is this a common issue? Does anyone have any suggestions for fixing this? My files are attached.
Mike Campbell, E.I.T., LEED AP O+M
Sustainability Specialist
Sustainable Solutions Corporation
Office: 610-569-1047<http://610-569-1047/>
Mobile: 609-923-1743<http://610-569-1047/>
www.SustainableSolutionsCorporation.com<http://www.sustainablesolutionscorporation.com/>
Sustainable Solutions Corporation is WBENC and BCorp Certified.
This email message and any attachments are for the sole use of the intended recipient(s) and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply email and destroy all copies of the original message and any attachments.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140708/140a4a45/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 171577 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140708/140a4a45/attachment.png>
More information about the Equest-users
mailing list