When DOE-2 (the base program under eQUEST) reports a wall as too thick or too dense, what
it's really saying is that it failed to find a Common Ratio between the three response
factors at the end of 100 time steps (hours). Response Factors are what DOE-2 uses to
model heat flows, where the three response factors (X,Y,Z) give the fraction of the heat
flow occurring each hour after the initial pulse. For the residual heat flows beyond 100
hours, DOE-2 uses the Common Ratio since all three response factors are decaying (so to
speak) at the same rate.
When the Common Ratio is still changing, then DOE-2 says that the wall is "too thick or
too dense". Such situations are caused not just by the thickness or density of the wall,
but also when there are anomalies in the thermal characteristics of the layers. For
example, I've found that for a foundation layer (which is where I've most often
encountered this problem), DOE-2 will accept a single layer of dirt 5.25 ft thick, but
once a layer of insulation is added, the dirt layer can only be 2 ft thick or less.
In the case cited below, what is the order of the 3 layers? Is it as written - plaster,
concrete, then air ? - or is it plaster, air, and then concrete?
In the latter case, it's the air layer that's probably limiting the allowable thickness of
the concrete. How are you modeling the air gap? If it's as a mass layer and not a
resistance layer, you might want to play around with its thermal characteristics to reduce
the discontinuity, and see if that helps. What I mean is that as long as the resistance
of the air layer is correct, adding some thermal mass to it (or "transferring it" from the
concrete :-)) might help. Although this might sound wrong, but it's probably better than
limiting the thickness or mass of the concrete just to avoid the dreadful "too dense or
too thick" error.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 7/29/2014 5:51 AM, Prasad S Wani wrote:
>
> Dear All,
>
> I am modelling a multilayer wall consisting of materials -- Cement Plaster, Medium
> weight concrete and Air.
>
> The total wall thickness is ~ 1.2 ft. However, a simulation error is obtained -- "Wall
> is too thick or too dense".
>
> Error persisted even when total wall thickness was increased by increasing _air gap
> thickness_.
>
> However, error did not occur when air gap thickness was reduced.
>
> It appears that reducing air gap reduces density of the wall (density varies directly
> with air gap).
>
> Kindly inform whether there is a method in eQUEST by which such simulation error (Wall
> is too thick or too dense) can be nullified.
>
> Thanks in advance.
>
> Regards
>
> Prasad
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140729/766fc08f/attachment.htm>
More information about the Equest-users
mailing list