[Equest-users] Cascading airflows in eQUEST
Bishop, Bill
bbishop at pathfinder-ea.com
Tue Jun 3 08:32:18 PDT 2014
I usually just model the two zones with an air wall in between them, and split the supply CFM between the zones (not necessarily evenly - you would favor the transfer-from zone as it would have conditioning priority). I also use different thermostat schedules for the transfer-to zone (as applicable) as it is usually designed to float more than the transfer-from zone. Both zones would be assigned to whatever system supplies the air to the transfer-from zone.
Regards,
Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[ASHRAE Certified logo - greenshot 2] [cid:image002.jpg at 01CF7F1F.78EEBFA0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[earth for signature]Sustainability - the forest AND the trees.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kathryn Kerns
Sent: Tuesday, June 03, 2014 11:16 AM
To: PKConsulting; Sami, Vikram
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Cascading airflows in eQUEST
This is just a suggestion and I haven't had time to investigate it yet, but I would think that the zone that the air is cascaded to could be represented by a PSZ system that uses the specified amount of zone transfer supply air with supply heating and cooling temperatures around 65 F heating and 75 F cooling and heating and cooling devices that are artificially constructed so they don't consume energy since you have already paid for the energy in the first zone. Its not perfect, but it might be close enough.
________________________________
From: Equest-users on behalf of PKConsulting
Sent: Mon 6/2/2014 4:05 PM
To: Sami, Vikram
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Cascading airflows in eQUEST
Hi Vik, no you can't. DOE2 is a static calculation and cannot exchange from zone to zone. The only way I can consider to try to mimic something would be to use one large zone for both and then reduce the amount of air changes in that zone compared to a normal input; and then try to widen the t-stat range for a lower load in that zone so it acts more 'neutraly' conditioned than a typical HVAC approach. Otherwise if you figure something out id like to learn what you did.
Pasha
Ph: 308-763-1593
On Jun 2, 2014, at 3:00 PM, "Sami, Vikram" <vikram.sami at zgf.com<mailto:vikram.sami at zgf.com>> wrote:
Is it possible to cascade airflow from one zone to another in eQUEST? I'm familiar with the OA from system function. Is there an OA from Zone command? I have a situation where we have significant makeup air from one zone coming into another.
Vikram Sami
BEMP, LEED BD+C
Associate Partner
ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com<mailto:vikram.sami at zgf.com>
925 Fourth Avenue, Suite 2400
Seattle, WA 98104
________________________________
The contents of this email and any attachments to it contain confidential and/or legally privileged information from Zimmer Gunsul Frasca Architects LLP or its affiliates. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, be aware that any disclosure, copying, distribution, or use of the information contained herein is strictly prohibited. If you received this transmission in error, please contact the sender and destroy the material in its entirety, whether in electronic or hard copy format.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140603/06688fbd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4717 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140603/06688fbd/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 4600 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140603/06688fbd/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2181 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140603/06688fbd/attachment-0001.jpg>
More information about the Equest-users
mailing list