G3.1.2.2 Equipment Capacities
David Griffin
dgriffin at etcgrp.com
Mon Jun 9 14:15:26 PDT 2014
Hmmmm...
I would like to know the name of the trainer, so I can make sure I don't take any of his/her courses (unfortunately this is not allowed on the list sever - don't mention name). Diviating from standard modeling practice to make the energy model numbers 'look' better is a horrible idea for many reasons!
I'm sure you are aware of them which is why you posted the question in the first place.
Yet another reason why energy modeling methodologies should be standardized.
Thanks for posting.
Sincerely,
David Griffin
ETC Group, LLC
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Monday, June 09, 2014 2:57 PM
To: David Griffin; equest-users at lists.onebuilding.org
Subject: RE: G3.1.2.2 Equipment Capacities
Another modeler in the office attended some training where they were recommending the second method described below (system sizing ratio to 1.15), as it would increase the baseline fan energy and therefore improve the energy savings calculation.
From: David Griffin [mailto:dgriffin at etcgrp.com]
Sent: Monday, June 09, 2014 4:50 PM
To: Bishop, Bill; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: G3.1.2.2 Equipment Capacities
Bill,
Every LEED model I've created employs the first method mentioned below, 'COOL-SIZING-RATI to 1.15, the HEAT-SIZING-RATI to 1.25 and the SYSTEM:SIZING-RATIO to 1.00' and I've never had a LEED reviewer call me out on it.
I'm curious how this questions came about. Did a LEED reviewer comment on it?
Sincerely,
David Griffin
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Monday, June 09, 2014 8:59 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: G3.1.2.2 Equipment Capacities
I made the comment below a while back on equest-users. Has anyone gotten any LEED comments that either confirm or challenge my interpretation?
Thanks,
Bill
My understanding has always been that the G3.1.2.2 oversizing requirement should be met by setting the COOL-SIZING-RATI to 1.15, the HEAT-SIZING-RATI to 1.25 and the SYSTEM:SIZING-RATIO to 1.00 for all baseline systems. The system sizing ratio acts as a multiplier on airflows as well as a multiplier on the cool and heat sizing ratios, so you could accomplish the cooling and heating oversizing by setting system sizing ratio to 1.15, the cool sizing ratio to 1.00 and the heat sizing ratio to 1.09. However, you would then be oversizing the airflow as well. While earlier versions of ASHRAE 90.1 did not elaborate on what exactly should be multiplied, 90.1-2010 specifically says "system coil capacities" shall be oversized. So we should be leaving the system sizing ratio at 1.00 and only oversizing via the cool and heat sizing ratios.
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[ASHRAE Certified logo - greenshot 2] [cid:image002.jpg at 01CF83F5.A42D4490]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[earth for signature]Sustainability - the forest AND the trees.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140609/73153c1b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4717 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140609/73153c1b/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2181 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140609/73153c1b/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 4600 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140609/73153c1b/attachment.png>
More information about the Equest-users
mailing list