We do not know what type of climate your particular building is in, nor the way you operate the building. If you are in a mild climate (such as Southern California), you will see very little difference. if you do no operate your building 24/7, this too will lower your savings. And finally, you are probably getting more heating through your ventilation system than you are through you wall..
Consider these things.
John R. Aulbach, PE
Los Angeles, CA, USA
On Sunday, June 15, 2014 6:15 AM, Byron Burns <B.Burns at ha-inc.com> wrote:
Hello Tugce,
It really depends on the building you are modeling and the climate. Is the building dominated by internal loads? The higher the internal loads, the less affect envelope improvements will have on the energy use of the building. What are the heating degree days for the climate you are modeling?
Review the LS-C and LS-B report to evaluate the change in heat flux through the building components you are evaluating. This should indicate whether the model is set up correctly, rather than looking at the overall heating load.
Byron D. Burns, EIT, BEMP
Energy Engineer, Building Sciences Studio
H&A Architects & Engineers | www.ha-inc.com
d: (804) 420-1622 p: (804) 285-4171 f: (804) 217-8520
From:Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of tugçe ake
Sent: Sunday, June 15, 2014 9:02 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] U value-space heating
Dear All,
I modeled a building and I want to make a comparison with different materials, which have different U values, for external wall. But when I change U value, space heating load does not change as expected. For example, I tried to make a comparison between two materials, their U values are 1,2W/m2K and 0,2W/m2K, and the result shows that space heating load is reduced by only 8%.
Is this result rational? or Is there something wrong?
Thanks
Tugce
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140615/c482ddef/attachment.htm>
More information about the Equest-users
mailing list