One more thing...
If the pool is uncovered, the night sky radiation losses are not
insignificant. I believe that the "energyexperts" data takes this into
account.
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 3/29/2014 2:00 PM, Riley Beise wrote:
>
> Tom,
>
>
> Here's how I do it: (geez it looks long now that I've written it, but
> it's really not bad and I feel it does a good job)
>
> 1.Determine your peak evaporation rate (lb/hr) for the pool(s) within
> the natatorium
>
> a.Should be available from the pool designers or if not, see the
> Natatorium section in ASHRAE Handbook -- HVAC Applications section 5
> (Places of Assembly).
>
> b.Values will depend largely on water temperature and peak "Activity
> Factor" expected, but ballpark values are
>
> i.Lap pool: 0.05 lb/hr per ft² of water surface area
>
> ii.Leisure pool: 0.2 lb/hr per ft² of water surface area (warmer than
> lap and higher activity factor (more splashing = more evaporation))
>
> iii.Swirl or Hot Tub: 0.4 lb/hr per ft² of water surface area (hot,
> with jets)
>
> 2.Create a schedule to represent the pool evaporation rate during
> different usage scenarios (different activity factors, different
> evaporation rates).
>
> a.I use three modes of operation:
>
> i.Unoccupied and uncovered: approx. 0.3
>
> ii.Occupied and low use: approx. 0.7
>
> iii.Occupied and high use: 1.0
>
> 3.Create an Internal Energy Source within your natatorium space with
> the magnitude equal to the peak evaporation rate, but in Btu/hr (1000
> Btu/lb of water evaporating), and make the load 100% latent, 0%
> sensible like so:
>
> 4.Now create a process heating load on your heating water loop and
> apply the same schedule. The magnitude of the load is calculated as:
>
> a.Pool water heat loss to evaporation (equal to evaporation "Internal
> Energy Source"), PLUS
>
> b.Heating energy required to heat the makeup water from DCW inlet up
> to pool water temperature. This is accounting for heating the fresh
> water that is replacing the water lost due to evaporation (in the
> range of 140 Btu/hr per lb/hr of water depending on your makeup water
> and pool water temps)
>
> c.Note that this assumes that 100% of the heat required for
> evaporation at the pool's surface is provided by the pool water's
> heat, where in reality it is expected that some component comes from
> the air, though I expect it is a small component.
>
> 5.Set min and max RH in your AHU and you're done.
>
> And if you felt there was significant heat loss through the pool wall
> to the ground, you could add that in as well, though I think that it
> probably isn't when compared to the energy involved in evaporation.
>
> *Riley Beise*, P.Eng., BEMP, LEED Green Associate
>
> Energy Analyst
>
> *AME Consulting Group*
>
> *721 Johnson Street*
>
> *Victoria, BC, V8W 1M8*
>
> p. 250-382-5999
>
> *From:*RobertWichert [mailto:robert at wichert.org]
> *Sent:* Saturday, March 29, 2014 8:44 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Natatorium/Pool
>
> Well, it's not EQuest, but it's on topic:
>
> http://energyexperts.org/CalculatorsTools/PoolEnergyUseCalculator.aspx
>
>
>
> Robert Wichert P.Eng. LEED AP BD&C
> +1 916 966 9060
> FAX +1 916 966 9068
>
>
>
>
>
>
>
> ===============================================
>
> On 3/28/2014 11:49 AM, Tom Mickley wrote:
>
> Does anyone have a simple, easy way to model an in ground pool and
> spa for a natatorium?
>
> Thanks,
>
> Tom Mickley
>
> Mechanical Engineer CEM
>
> The K Company
>
> Cell 330-760-3994
>
> Office 330-773-5125
>
>
>
>
> _______________________________________________
>
> Equest-users mailing list
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140330/e8e96e7b/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 7902 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140330/e8e96e7b/attachment-0002.png>
More information about the Equest-users
mailing list