[Equest-users] Significantly Higher Heating and Cooling Energy Consumption in EnergyPlus When Compared to eQUEST
Joe Huang
yjhuang at whiteboxtechnologies.com
Fri May 2 15:15:21 PDT 2014
Simge,
I feel compelled to respond since you mentioned me so prominently in
your post :-)
I think you're bringing up a very germaine question, and indeed it's one
that in my opinion needs further study, i.e.,
how does EnergyPlus compare with eQUEST or other building energy
simulation programs in their modeling results?
The LBNL paper you cited is a summary paper from a SimBuild Conference
in 2008 that only skimmed the findings from a
year-long effort supported by the California Energy Commission. I've put
the full report on the Web, along with a later study
I did last year as part of an EnergyPlus Feasibility Study by AutoDesk
done for Southern California Edison that you might find
equally interesting:
http://www.whiteboxtechnologies.com/download_AutoDesk_EP_feasib_rpt.htm
The second study was under wraps for a long time, but I received
clearance from SCE to release it two months ago.
My part of the study is strictly the EnergyPlus to DOE-2.2 comparison
pp. 57 -98, and I have no opinions one way or
the other in respect to the rest of the study. My task was to take
several DEER prototypes (office, residential, and retail)
modeled in eQUEST/DOE-2.2 and convert them to EP 7.X. Compared to what
I saw in the 2007 study, the discrepancies
in heating energy consumption were even more striking, probably because
all the buildings were modeled in southern
California climates. I was getting consistently from a 5:1 to a 20:1
difference in heating energies (DOE-2 high, EP low).
Following up on Jeff's earlier comment, diagnosing the differences
between two simulation programs requires a lot of
time, experimentation, and often in-depth study of the source codes. In
the 2007 paper, I mentioned somewhere between
15 and 20 areas of modeling differences with significant effects on the
results.
It's been 7 years since the first study, and I've been disappointed by
the lack of progress. Some of it is understandable, since
speaking frankly, there are a very limited number of people with
sufficient knowledge and interest across two programs to make heads or
tails out of these comparisons. But it is a very important issue, not
just from technical curiosity, but because a lot of
money have been invested based on what these programs say, so if they
give significantly different results, policy makers would
like to know what's going on and ideally, what is the ground truth?
I don't want to sound like a modern-day Cassandra, and I don't have
enough resources or time to pursue this as a private
adventure. However, I hope that public institutions will see the need
and benefit, and support some serious work in this area.
I know that you (Simge) or I are not the only people who've wrestled
with this problem. I would like to hear the experiences of
others (not you, Jeff, I already know what you would say :-) ). Since
all the efforts I've heard of are going from eQUEST
to EnergyPlus, not the other way around, the domain knowledge is
probably higher on the eQUEST/DOE-2 side. Therefore,
it would be most valuable to get the EnergyPlus experts to chime in on
the nuances of EnergyPlus modeling of which we
may be lacking. For the same reason, you might consider posting your
message to the EnergyPlus_Support bulletin board
as well.
See, Simge, now you got me wasting a couple of hours on a Friday afternoon!
I'm not sure when I would have time to look at your input files, but if
I see anything I'll let you know.
Joe
On 5/1/2014 1:35 PM, Simge Andolsun wrote:
> Dear eQUEST users (Particularly Dear Joe Huang),
>
> Please find the attached eQUEST and EnergyPlus files. They represent
> identical cases for comparison of the two programs. The runs are
> conducted for Los Angeles. The heating and cooling consumption of
> EnergyPlus file are, however, unreasonably higher than that of EQUEST.
> It is particularly strange that heating occurs in early morning
> time during the summer in EnergyPlus whereas no heating occurs in
> eQUEST during these hours.
>
> We need our results not to deviate extremely from eQUEST when we
> start using EnergyPlus. That is why, I am conducting this comparative
> analyses for cases representing identical conditions. I would
> appreciate it very much if you could examine these files and let me
> know whether there is anything I can do to make the results of these
> cases in the two programs as close as possible to each other.
>
> Dear Joe Huang,
>
> Please see the attached charts that show the hourly variation of
> temperatures in the system nodes and hourly energy consumption. There
> is definitely something weird going on in the early morning hours when
> the system just starts working. I have read your paper in the link
> below. Below is a section from your paper that I have paid particular
> attention to. Might I be having a similar issue in my case?
> http://gundog.lbl.gov/dirpubs/SB06/huang.pdf.
>
> /"Heating to the cooling setpoint/. Temperature plots revealed that at
> times during the shoulder seasons, /EnergyPlus /had difficulty in
> picking between the heating or cooling season control logic. This
> resulted in the supply air being heated to the cooling, rather than
> the heating, setpoint during the morning hours. This problem was
> corrected by improving the setpoint manager in /EnergyPlus/."
>
> Looking forward to hearing from you,
>
> Best Regards,
> Simge Andolsun, PhD.
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG