[Equest-users] Issue with drawings zones in wizard

Samantha MacHardy SMacHardy at pemi.com
Tue May 6 11:45:34 PDT 2014


I typically find that using ‘via coordinates’ rather than directly above works a lot better for me when lining up my shells. Maybe this will work for you!

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael Campbell
Sent: Tuesday, May 06, 2014 2:12 PM
To: John Aulbach; Jeremy McClanathan; David C. Fishel; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Issue with drawings zones in wizard

Thanks for the advice, I will try that.

Mike Campbell, E.I.T., LEED AP O+M
Sustainability Specialist
Sustainable Solutions Corporation
Office: 610-569-1047<http://610-569-1047/>
Mobile: 609-923-1743<http://610-569-1047/>
www.SustainableSolutionsCorporation.com<http://www.sustainablesolutionscorporation.com/>
Sustainable Solutions Corporation is WBENC and BCorp Certified.

This email message and any attachments are for the sole use of the intended recipient(s) and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply email and destroy all copies of the original message and any attachments.

From: John Aulbach [mailto:jra_sac at yahoo.com<mailto:jra_sac at yahoo.com>]
Sent: Tuesday, May 06, 2014 2:11 PM
To: Michael Campbell; Jeremy McClanathan; David C. Fishel; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Issue with drawings zones in wizard

I have fiddled with such difficulties. Try restating the Z component within the Building coordinat system (absolute Z).

For some reason, the "immediately above" doesnt always work for me. But redefining the Z component does.

John R. Aulbach, PE

From: Michael Campbell <mike at sustainablesolutionscorporation.com<mailto:mike at sustainablesolutionscorporation.com>>
To: Jeremy McClanathan <jmcclanathan at cdiengineers.com<mailto:jmcclanathan at cdiengineers.com>>; David C. Fishel <David_Fishel at rlfae.com<mailto:David_Fishel at rlfae.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Sent: Tuesday, May 6, 2014 9:52 AM
Subject: Re: [Equest-users] Issue with drawings zones in wizard

Thank you for the advice.  I was able to fix that issue.  However, now another issue has come up.  I’ve created two shells in the wizard – one for the first floor and one for the second floor.  I have defined the 2nd florr to be “immediately above” the 1st floor.  However, when I move to the detailed mode, the 2nd floor appears to be on the same plane as the 1st floor.  It appears like it does not recognize that there is a second floor and the zoning is distorted.  No matter what I try, I cannot seem to get the 2nd floor shell to move.  Any advice?

Mike Campbell, E.I.T., LEED AP O+M
Sustainability Specialist
Sustainable Solutions Corporation
Office: 610-569-1047<http://610-569-1047/>
Mobile: 609-923-1743<http://610-569-1047/>
http://www.sustainablesolutionscorporation.com/
Sustainable Solutions Corporation is WBENC and BCorp Certified.

This email message and any attachments are for the sole use of the intended recipient(s) and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply email and destroy all copies of the original message and any attachments.

From: Jeremy McClanathan [mailto:jmcclanathan at CDiengineers.com<mailto:jmcclanathan at CDiengineers.com>]
Sent: Tuesday, May 06, 2014 12:30 PM
To: 'David C. Fishel'; 'Michael Campbell'; 'equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>'
Subject: RE: [Equest-users] Issue with drawings zones in wizard

I have come across similar issues when a zone accidentally had two vertices with the same point.  Sometimes it helps to run the simulation, then open the BDL file and search for “Error”, or “Warning”.

Jeremy

Jeremy McClanathan, P.E., BEMP, HFDP, LEED AP
Mechanical Engineer

[cid:image001.jpg at 01CF6939.D62735E0]
19203 36th Avenue W, Suite 200
Lynnwood, WA 98036

T: 425.672.1071
D: 425.712.2198

From: David C. Fishel [mailto:David_Fishel at rlfae.com]
Sent: Tuesday, May 06, 2014 6:01 AM
To: Michael Campbell; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Issue with drawings zones in wizard

If you are still using Equest 3.64 it has a limit on size and this may be your problem.  The limits were expanded in the latest version 3.65.

You can combine similar zones without a loss of accuracy and simplify your model.

Hope this helps

-David

David C. Fishel, PE
Senior Energy Analyst

RLF | architecture engineering interiors
4750 New Broad Street, Orlando, FL 32814
p 407.730-8600 | f 407.730-3603| http://www.rlfarchitects.com/

P Please consider the environment before printing this e-mail


From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael Campbell
Sent: Tuesday, May 06, 2014 8:54 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Issue with drawings zones in wizard

So I have a new project in which I have completed drawing the first floor outline and zones.  See below image showing the completed floor plan.

[cid:image002.jpg at 01CF6939.D62735E0]

However, when I go to the detailed mode, many of these zones are not defined.  It looks like they just do not exist.  See below image.

[cid:image003.jpg at 01CF6939.D62735E0]

Has anyone encountered this issue before?  I’ve tried re-drawing the zones and nothing seems to be working.

Mike Campbell, E.I.T., LEED AP O+M
Sustainability Specialist
Sustainable Solutions Corporation
Office: 610-569-1047<http://610-569-1047/>
Mobile: 609-923-1743<http://610-569-1047/>
http://www.sustainablesolutionscorporation.com/
Sustainable Solutions Corporation is WBENC and BCorp Certified.

This email message and any attachments are for the sole use of the intended recipient(s) and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply email and destroy all copies of the original message and any attachments.



This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws.  If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments.  If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies.

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140506/d9f1aee0/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1622 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140506/d9f1aee0/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 129768 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140506/d9f1aee0/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 97611 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140506/d9f1aee0/attachment-0008.jpg>


More information about the Equest-users mailing list