[Equest-users] Space by Space LPD requirements for 90.1 modeling

Cam Fitzgerald cam at energyopportunities.com
Fri May 23 05:29:41 PDT 2014


Dear Javid,

 

You are right to question this review comment. Interior lighting is tradable
when using energy simulations not the prescriptive 90.1 requirements. I
suggest you send an inquiry to the review team requesting confirmation of
the requirement and further explanation. You should explain your
understanding of the Appendix G requirements and briefly explain how the
lighting is modeled in the baseline and proposed case. Clarifying the issue
before you make any changes to the model and resubmit could save a lot of
headache (and time). Good luck!

 

 

Cam Fitzgerald

 

Energy Opportunities/a 7group company

1200 E Camping Area Rd, Wellsville, PA 17365

 

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Javed Iqbal
Sent: Friday, May 23, 2014 7:53 AM
To: equest-users
Subject: [Equest-users] Space by Space LPD requirements for 90.1 modeling

 

Dear All,

 

Recently i have received a comment from design team peer reviewer on
applicability of space by space lighting power density for 90.1 appendix G
compliance modeling for manufacturing facility and given as follows:

 

"Space by Space" method can only be used if the actual proposed design meets
the space by space requirements for each included space type.

 

I found similar discussion happened on 23/5/12- Building Area Method 90.1
(great insight from Nick) but didn't noticed any such requirements like
mentioned above. I am clueless on this and can't even verify if this is a
valid comment.

 

I would appreciate if someone could guide me on this.

 

Thanks in advance,

 

 

-- 

 

Javed Iqbal, LEED AP, CEA

Sr. Energy Analyst 

 

 

 

 

 