[Equest-users] Oversized cooling
Gonzalo Lema
GLema at sumacinc.com
Tue Nov 25 11:30:29 PST 2014
Hi Vikram,
Actually, the proposed design has a 90 ton chiller, so the 77.25 tons maximum cooling load should be fine. My concern is that the auto-size PVAVS for baseline design is too big compared to the load and to the proposed design.
Is this something a LEED reviewer might object?
Thanks.
SUMAC
Gonzalo Lema | Mechanical Engineer | LEED GA
Tel: +1.773.857.7906 Ext 7009 (Chicago, USA)
Tel: +1.305.814.8805 (Miami, USA)
Tel: +511.253.5355 (Lima, Perú)
Tel: +593.4.600.0613 (Guayaquil, Ecuador)
Tel: + 571.3151985 (Bogotá, Colombia)
glema at sumacinc.com<mailto:glema at sumacinc.com>
www.sumacinc.com<http://www.sumacinc.com/>
From: Sami, Vikram [mailto:vikram.sami at zgf.com]
Sent: Tuesday, November 25, 2014 1:19 PM
To: Gonzalo Lema; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Oversized cooling
Curious.
I do think the higher load seems to be more like what you should expect for a building this size (7501 kBTU/h = 625 tons. For a 102,000 ft2 building that's 163 ft2/ton). That might be slightly oversized for Ft Carson, although Colorado springs gets hot in the summer. Not sure what your building loads are, but 163 ft2/ton is not unheard of for a heavy use building. I would expect something more in the range of 250-300. So the question is why is the maximum cooling load reporting as only 927 kBTU/hr (77.25 tons = 1320 ft2/ton)
Just my two cents from looking at this for five minutes - I might be wrong.
Vikram Sami
BEMP, LEED BD+C
Associate Partner
ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com<mailto:vikram.sami at zgf.com>
925 Fourth Avenue, Suite 2400
Seattle, WA 98104
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Gonzalo Lema
Sent: Monday, November 24, 2014 12:25 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Oversized cooling
Hi,
I have a problem with the cooling capacity. The Max cooling load is 927 kbtu/hr, but the cooling capacity is 7501 kbtu/h. I auto-sized the equipment (system and cooling coil) for 1.00, but I don't understand why the factor seems to be 8x.
[cid:image001.jpg at 01D008B3.E85FE030]
[cid:image002.png at 01D008B3.E85FE030]
The system fan Works in part-load 0-20% all the time:
[cid:image003.png at 01D008B3.E85FE030]
Does anybody knows what could be causing this?
Thanks.
SUMAC
Gonzalo Lema | Mechanical Engineer | LEED GA
Tel: +1.773.857.7906 Ext 7009 (Chicago, USA)
Tel: +1.305.814.8805 (Miami, USA)
Tel: +511.253.5355 (Lima, Perú)
Tel: +593.4.600.0613 (Guayaquil, Ecuador)
Tel: + 571.3151985 (Bogotá, Colombia)
glema at sumacinc.com<mailto:glema at sumacinc.com>
www.sumacinc.com<http://www.sumacinc.com/>
From: Dante Garcia
Sent: Monday, November 24, 2014 10:24 AM
To: Gonzalo Lema
Subject: RE: eQuest - Fort Cartson
Hola Gonzalo, no he podido encontrar el error hasta el viernes que estuve avanzando.
Ahora he estado con otras prioridades, mañana puedo volver a revisar el proyecto.
Saludos,
Dante
SUMAC
Dante Garcia, LEED AP BD+C | Analista LEED Energía
Tel: +511.253.5355 Anexo 16 (Lima, Perú)
Cel: +51.989.685.769 (Lima, Perú)
Tel: +593.4.600.0613 (Guayaquil, Ecuador)
Tel: + 571.3151985 (Bogotá, Colombia)
Tel: +1.773.857.7906 (Chicago, USA)
dgarcia at sumacinc.com<mailto:dgarcia at sumacinc.com>
www.sumacinc.com<http://www.sumacinc.com/>
De: Gonzalo Lema
Enviado el: lunes, 24 de noviembre de 2014 11:17 a.m.
Para: Dante Garcia
Asunto: RE: eQuest - Fort Cartson
Buen día,
¿Alguna novedad?
Yo sigo revisando también.
Saludos
SUMAC
Gonzalo Lema | Mechanical Engineer | LEED GA
Tel: +1.773.857.7906 Ext 7009 (Chicago, USA)
Tel: +1.305.814.8805 (Miami, USA)
Tel: +511.253.5355 (Lima, Perú)
Tel: +593.4.600.0613 (Guayaquil, Ecuador)
Tel: + 571.3151985 (Bogotá, Colombia)
glema at sumacinc.com<mailto:glema at sumacinc.com>
www.sumacinc.com<http://www.sumacinc.com/>
From: Gonzalo Lema
Sent: Friday, November 21, 2014 5:52 PM
To: Dante Garcia
Subject: RE: eQuest - Fort Cartson
Como va?
Encontraste algo mas?
Buen finde.
SUMAC
Gonzalo Lema | Mechanical Engineer | LEED GA
Tel: +1.773.857.7906 Ext 7009 (Chicago, USA)
Tel: +1.305.814.8805 (Miami, USA)
Tel: +511.253.5355 (Lima, Perú)
Tel: +593.4.600.0613 (Guayaquil, Ecuador)
Tel: + 571.3151985 (Bogotá, Colombia)
glema at sumacinc.com<mailto:glema at sumacinc.com>
www.sumacinc.com<http://www.sumacinc.com/>
From: Dante Garcia
Sent: Thursday, November 20, 2014 5:21 PM
To: Gonzalo Lema
Subject: eQuest - Fort Cartson
Gonzalo, te envío el eQuest que revisé, todavía no encuentro el error, solo edité un poco el primer piso ya que dos zonas se sobreponían, mañana seguré revisando y ver si encuentro algo, una consulta, viste este reporte, así son los cfm que deben tener cada zona o es bien alto?
Saludos,
Dante
[cid:image004.jpg at 01D008B3.E85FE030]
SUMAC
Dante Garcia, LEED AP BD+C | Analista LEED Energía
Tel: +511.253.5355 Anexo 16 (Lima, Perú)
Cel: +51.989.685.769 (Lima, Perú)
Tel: +593.4.600.0613 (Guayaquil, Ecuador)
Tel: + 571.3151985 (Bogotá, Colombia)
Tel: +1.773.857.7906 (Chicago, USA)
dgarcia at sumacinc.com<mailto:dgarcia at sumacinc.com>
www.sumacinc.com<http://www.sumacinc.com/>
ZGF Email Disclaimer<https://www.zgf.com/ZGF_Email_Disclaimer.html>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141125/32b8f6ab/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 43505 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141125/32b8f6ab/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 20625 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141125/32b8f6ab/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 39268 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141125/32b8f6ab/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 36650 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141125/32b8f6ab/attachment-0001.jpg>
More information about the Equest-users
mailing list