[Equest-users] Fan cycling when unoccupied

Greenberg, Ari AGreenberg at brplusa.com
Thu Aug 13 12:45:14 PDT 2015


Hi Steve,

I believe the requirement comes from Appendix G:  "G3.1.2.4 Fan System Operation. Supply and return fans shall operate continuously whenever spaces are occupied and shall be cycled to meet heating and cooling loads during unoccupied hours."

Hope that helps.
Ari


[[BR+A]]        Ari Greenberg
HVAC Engineer
Bard, Rao + Athanas Consulting Engineers, LLC
10 Guest St., 4th Floor?  |  Boston,? Massachusetts ?02135
e agreenberg at brplusa.com<mailto:agreenberg at brplusa.com>   t 617.925.8298   |   www.brplusa.com<http://www.brplusa.com>
Boston  |   New York  |   Philadelphia  |   DC  |   Miami  |   Chicago  |   St. Louis

INNOVATION |  EXPERIENCE |  PROVEN SUCCESS

This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy or alter this email.
P  Please consider the environment before printing this e-mail
[[Facebook]]<https://www.facebook.com/BardRaoAthanas> [[LinkedIn]] <https://www.linkedin.com/company/br-a-consulting-engineers>  [[twitter]] <https://twitter.com/BRplusA>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Steve Jacobs
Sent: Thursday, August 13, 2015 3:30 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fan cycling when unoccupied

Does anyone know if the requirement for the OA to remain off when the fans cycle after hours comes from somewhere in ASHRAE, or is just something that LEED requires.

Thanks,
Steve
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150813/fe8b5867/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo2011.gif
Type: image/gif
Size: 2532 bytes
Desc: logo2011.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150813/fe8b5867/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: facebook.gif
Type: image/gif
Size: 1317 bytes
Desc: facebook.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150813/fe8b5867/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: linkedin.GIF
Type: image/gif
Size: 1295 bytes
Desc: linkedin.GIF
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150813/fe8b5867/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: twitter.gif
Type: image/gif
Size: 1351 bytes
Desc: twitter.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150813/fe8b5867/attachment-0003.gif>


More information about the Equest-users mailing list