[Equest-users] Fan cycling when unoccupied

Steve Jacobs sjacobseng at gmail.com
Thu Aug 13 14:36:43 PDT 2015


Great, Thanks for the quick responses guys.

 

From: Daric Adair [mailto:Daric.Adair at hei-eng.com] 
Sent: Thursday, August 13, 2015 2:55 PM
To: Greenberg, Ari; 'Steve Jacobs'; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Fan cycling when unoccupied

 

Hello Steve;

 

To tag onto Ari’s response only because it was a semi-vague question. 

 

If this is a general type question: ASHRAE 62.1-2010 Section 5.3 calls for Ventilation ‘whenever occupied’. Tagging onto this ASHRAE 90.1-2010 Section 6.4.3.4.2 states that all outside air and exhaust damper shut when systems or spaces served are not in use. (paraphrasing). Different reasons, but effective ventilation when the space is occupied used, and minimize energy the spaces aren’t used. Keeps occupants healthy with OA and minimizes energy consumption.

 

If this is a modeling / appendix G type question, the Ari nailed it.

 

 

Thanks,

DARIC R. ADAIR  PE, C.E.M. 
Henderson Engineers, Inc. | Mechanical Engineer, Energy Analyst 
dir 913 742 5530  tel 913 742 5000  fax 913 742 5001  tx id #F-001236  email daric.adair at hei-eng.com   <http://www.hei-eng.com/> www.hei-eng.com 
Licensed in KS. 

 

From: Greenberg, Ari [mailto:AGreenberg at brplusa.com] 
Sent: Thursday, August 13, 2015 2:45 PM
To: 'Steve Jacobs' <sjacobseng at gmail.com>; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Fan cycling when unoccupied

 

Hi Steve,

 

I believe the requirement comes from Appendix G:  “G3.1.2.4 Fan System Operation. Supply and return fans shall operate continuously whenever spaces are occupied and shall be cycled to meet heating and cooling loads during unoccupied hours.”

 

Hope that helps.

Ari

 

	
 


 [BR+A] 

Ari Greenberg
HVAC Engineer 


Bard, Rao + Athanas Consulting Engineers, LLC 
10 Guest St., 4th Floor​  |  Boston,​ Massachusetts ​02135
 <mailto:agreenberg at brplusa.com> e agreenberg at brplusa.com   t 617.925.8298   |    <http://www.brplusa.com> www.brplusa.com 
Boston  |   New York  |   Philadelphia  |   DC  |   Miami  |   Chicago  |   St. Louis 

 


INNOVATION |  EXPERIENCE |  PROVEN SUCCESS 

 


This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy or alter this email. 


P  Please consider the environment before printing this e-mail 


 <https://www.facebook.com/BardRaoAthanas> [Facebook]  <https://www.linkedin.com/company/br-a-consulting-engineers>  [LinkedIn]  <https://twitter.com/BRplusA>  [twitter]

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Steve Jacobs
Sent: Thursday, August 13, 2015 3:30 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fan cycling when unoccupied

 

Does anyone know if the requirement for the OA to remain off when the fans cycle after hours comes from somewhere in ASHRAE, or is just something that LEED requires.

 

Thanks,

Steve

 

  _____  


This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hei-eng.com.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150813/1c37a467/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2532 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150813/1c37a467/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1317 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150813/1c37a467/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1295 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150813/1c37a467/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1351 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150813/1c37a467/attachment-0003.gif>


More information about the Equest-users mailing list