[Equest-users] Evaporative Cooling on VAV

Jones, Christopher Christopher.r.Jones at wspgroup.com
Thu Aug 27 09:03:32 PDT 2015


Steve,
You could try setting the economizer to be on for all cooling hours.
OA-CONTROL = TEMP
DRYBULB-LIMIT = 99
$ don’t specify ECONO-LOW-LIMIT

If it’s a DX system:
ECONO-LOCKOUT = NO

..
[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0065

www.wspgroup.com<http://www.wspgroup.com/>

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Steve Jacobs
Sent: Thursday, August 27, 2015 11:53 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Evaporative Cooling on VAV

I have a building with a VAV system that has evaporative cooling with chilled water supplemental cooling. Is there a way to get eQuest to run the VAV at 100% outdoor air whenever it is in cooling mode but at minimum outdoor air in heating mode?


________________________________

You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150827/baf4c036/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150827/baf4c036/attachment.png>


More information about the Equest-users mailing list