[Equest-users] Title 24 2013 Baseline Chiller (Path A or B)
Philip Kennedy
philip at kiltechcontrols.com
Wed Feb 4 12:27:20 PST 2015
Matthew it is highly recommended you obtain data for the actual proposed
chiller in order to receive the right answer. There is huge variability in
the unloading characteristics of different chiller technologies.
For example the chart below depicts two VFD chillers of equal capacity. The
solid line chiller is a single compressor VFD machine and the dotted line is
a three compressor magnetic bearing unit.
One curve DOES NOT fit all.
I suggest you reach out to the equipment vendors and have each of them
provide the necessary data runs. A help spreadsheet to aid the collection of
data can be found:
http://www.taylor-engineering.com/downloads/cooltools/TE%20Chiller%20Bid%20F
orm%20v1.62.xlsm
Regards Philip
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Matthew Alvarez
Sent: February-04-15 1:38 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Title 24 2013 Baseline Chiller (Path A or B)
Greetings eQuest people,
I think I have a quick one for you that I could not find in the forums:
A chiller that has burned out is being replaced. The new baseline chiller is
the (CA Title 24 2013) 110.2-D chiller (path A or B). To calculate the
savings above T24 baseline, I first need to meet both the IPLV and kW/Ton
minimums for this baseline chiller. Does this theoretical minimum/baseline
chiller exist as a selection in eQuest somewhere? Is there a 'typical'
chiller (curve and efficiency) that can be downloaded/imported and used for
this purpose that is industry accepted?
Any suggestions?
Thanks in advance,
Matthew Alvarez, LEED AP
Energy Engineer
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150204/731aebb8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: application/octet-stream
Size: 650122 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150204/731aebb8/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 214818 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150204/731aebb8/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 232802 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150204/731aebb8/attachment-0001.png>
More information about the Equest-users
mailing list